[RE-wrenches] EGC for Enphases
August Goers
august at luminalt.com
Fri Jul 5 14:13:54 PDT 2013
Hi Dave,
I'm not sure I'm understanding your scenario clearly but I'll take a crack
at it. The Enphase system should have a bare #6 GEC for each micro and can
then transition to a #8 green GEC once in conduit and run all the way back
to the main ground electrode system. The #6 and #8 should be irreversibly
crimped together since the GEC needs to be continuous. Certainly it is not
okay for the neutral in the Lennox panel to be bare unless it is somehow a
main panel. You could run the DC GEC along with the other conductors and
it can serve as a dual purpose GEC and equipment grounding conductor per
2011 NEC 690.47(C)(3).
Best,
August
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Wednesday, July 03, 2013 6:26 AM
To: RE-wrenches
Subject: [RE-wrenches] EGC for Enphases
All,
I was just looking at small 4-module Andalay (Enphase 190) system tying
into one of the Lennox solar-ready air conditioners. The engineer had
specified the 690.47(C) GEC be run directly from the array down to the
existing electrode. Running from the inverters is a 2+G wire to the Lennox
panel; they are using the uninsulated ground as the circuit neutral. It
seems to me that this violates 200.7 (grounded conductor marked white or
grey). Also, 250.134(B) (EGC run with circuit conductors), about which the
engineer states "I have been studying the NEC on this and I believe that
the intent is to permit the ground to be carried with the current carrying
conductors, not require."
Am I missing something?
Thanks,
Dave
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list