[RE-wrenches] Battery bank during peak times
SunHarvest
eric at harvesthesun.com
Tue Jun 25 10:27:07 PDT 2013
Hi Jesse,
If I read this correctly your customer is wanting to go off-grid during peak hours. I recently went through this same thing with a customer. I received feedback from an old SMA tech and some Wrenchers (thread titled "Battery Back-up and Grid Tie"). Here's what I learned:
1. Inverters are more efficient at inverting than charging, anywhere from 5-10%. Add to that about 10% transmission loss...you'll always have significant energy losses associated with trying to put back that power that you're drawing out during those peak hours. Energy loss = $$ loss.
2. Compare the utility peak kWh cost against the cost of cycling the battery bank. Just for an example, let's say for a 48V system you're using 150Ah 12V Trojan AGMs $2000 for 8 batteries. If the specs say those batteries, at 50% discharge, get 1000 cycles in their lifetime, that's $2.00 per cycle. 300Ah X 48V X 50% = 7.2kWh. $2/7.2kWh = $0.28/kWh. Add to that 20% round-trip efficiency losses, you're up to $0.33/kWh. What else does daily, unnecessary cycling add: Extra maintenance? Shortened life so probably should factor in some replacement cost?...
3. Murphy's law says that the power will go out at the end of one of these non-essential discharge cycles. Then what?
Probably not worth it.
Eric Stikes
SunHarvest
530-798-3738
----- Original Message -----
From: Jesse Dahl
To: RE-wrenches
Sent: Monday, June 24, 2013 8:50 PM
Subject: [RE-wrenches] Battery bank during peak times
Hello,
I was contacted by a local co-op about installing a PV system at their office. At first they wanted a straight grid-tied system, and after they received the bid they changed their minds and now want a battery based system price. What they want now is a system that will allow them to draw the battery bank down starting at 5pm during their peak demand time. Has anyone worked on or installed a system of this type?
Thanks as always!
Jesse
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130625/41433a9d/attachment-0003.html>
More information about the RE-wrenches
mailing list