On one installation, I had the same error cod issue.  The project also used
the M190 inverters.  The issue ended up being a loose connection between one
of the inverter-to-inverter connections.  After re-checking all of the
connections, and making sure the connection was tight, the error code did
not come up again.

Alan Ross

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, November 26, 2012 1:46 PM
To: RE-wrenches
Subject: [RE-wrenches]  Enphase voltage out of range errors

Friends:

We have one site that is experiencing ongoing problems with errors
indicating, "AC Voltage Out Of Range."  This has occurred on two of 17 M190
inverters.  Apparently the voltage is not really out of range, the inverter
is erroneously reporting.

I have one replacement in hand and was just about to drive the 2 hours to
replace it when another inverter indicated the same problem.  I ordered a
second replacement.

I fear that soon after I return to my shop from the job I will see another
inverter with this problem.  Has anyone else experienced this error?

Thanks in advance,

William

Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





More information about the RE-wrenches mailing list