[RE-wrenches] PV direct pump under 30V and conduit in building

Kent Osterberg kent at coveoregon.com
Thu May 3 10:18:14 PDT 2012


Jason,

690.31(A) permits PV wiring for circuits below 30 volts to be installed 
in accessible locations without conduit or raceways. But 690.31(E) 
requires the use of metal raceways for PV circuits inside a building. It 
does not require EMT. It specifically allows MC cable. Unless there are 
local codes specifying otherwise, MC cable should be allowed. Even that 
is overkill for a small 12-volt module.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 5/3/2012 9:34 AM, Jason Szumlanski wrote:
> I'd like some help with code references for an inspector that is 
> requiring EMT for a 12V PV panel that runs a solar water heating 
> circulation pump. The wiring is run through the attic and down to the 
> pump near the water heater. I've never ran into this before (but I 
> have run into this inspector). :)
>
> Jason Szumlanski
> Fafco Solar
>