William Miller
william at millersolar.com
Fri Sep 9 09:10:47 PDT 2011
Allan:
I lowered the acceptance window to 80VAC. My recording Fluke 87 showed no
voltage sag even during the brief time the inverter tried to connect.
Wm
At 07:54 AM 9/9/2011, you wrote:
>We have done two XW systems, one off-grid with a generator. The generator
>is a 1970's-era Onan 12.5JC, a lovely beast of a workhorse with 18,000
>hours on it. The point of describing it is that this is about as basic an
>analog control as is available. AC output voltage on the unit was around
>114 VAC, slightly low. Frequency was right on. The XW would not latch to
>it, although the minimum AC2 in acceptable voltage was at the default
>setting, I believe 108V AC. Reducing the minimum AC2 in to round 100V
>cured the problem and it charged.
>
> From the number of responses to William's post, there may be a serious
> incompatibility issue with the XW's genstart/charging firmware, that
> shows up in different ways as different problems. I'd like to hear from
> Schneider about this.
>Allan
>
>Allan Sindelar