<font size=3>Allan:<br><br>
I lowered the acceptance window to 80VAC.  My recording Fluke 87
showed no voltage sag even during the brief time the inverter tried to
connect.<br><br>
Wm<br><br>
<br>
At 07:54 AM 9/9/2011, you wrote:<br>
<blockquote type=cite class=cite cite>We have done two XW systems, one
off-grid with a generator. The generator is a 1970's-era Onan 12.5JC, a
lovely beast of a workhorse with 18,000 hours on it. The point of
describing it is that this is about as basic an analog control as is
available. AC output voltage on the unit was around 114 VAC, slightly
low. Frequency was right on. The XW would not latch to it, although the
minimum AC2 in acceptable voltage was at the default setting, I believe
108V AC. Reducing the minimum AC2 in to round 100V cured the problem and
it charged. <br><br>
 From the number of responses to William's post, there may be a serious
incompatibility issue with the XW's genstart/charging firmware, that
shows up in different ways as different problems. I'd like to hear from
Schneider about this.<br>
Allan<br><br>