I hope i do not muddy the water here. if you have 3 phase delta, usually the
single phase transformer is larger, can you do the solar in split phase?
Also staying with the 3 phase, why not use a three pole service rated switch to
Line side tap, and use two poles for the single phase and the third pole for the
high leg. After the 3 pole switch, use a 2 pole switch for the wind turbine
(breaker in a box) , and a three pole sw in a box for the 3 phase solar. .
________________________________
From: John Wadley <wadleyjk at hotmail.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Wed, March 2, 2011 3:36:19 PM
Subject: [RE-wrenches] One renewable disconnect.
Wrenches,
I am designing a system with both wind and solar backfeed and I'm having
an issue with the utility. They say we need to have a single renewable
disconnect switch before the grid backfeed. The solar is designed to backfeed
3-phase through a meter, then a fused AC disconnect to the line-side to avoid
upsizing the MDP. The wind inverter output is 120/240V split-phase (10A) which
I had planned to do load-side backfeed through a wind meter with a seperate AC
disconnect since it was so small. To meet the single renewable disconnect
requirement, I'm thinking I may need to backfeed the wind on the load-side to
one of the three phases. I guess my question is can I use a single 5 pole fused
AC disconnect to control both with one switch handle or is that an NEC violation
wrt to merging separate systems within the same conduit? Or, should I keep them
in separate switch boxes with some kind of gang handle? I have a 3-phase
aggregation panel for the solar inverters (6 total, 2 per phase, 240 delta), but
if I integrate the wind there in order to simplify the AC disconnect issue, the
solar meter will register both solar and wind production. What is the best
practice in this situation?
Thanks,
John Wadley, MSEE, PE
NABCEP Certified Solar PV Installer (TM)
Wadley Engineering
214-557-3841
CONFIDENTIALITY: This communication, including attachments, is for the exclusive
use of the addressee(s) and may contain proprietary, confidential or privileged
information. If you are not the intended recipient, any use, copying,
disclosure, or distribution or the taking of any action in reliance upon this
information is strictly prohibited. If you are not the intended recipient,
please notify the sender immediately and delete this communication and destroy
all copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110302/4bb9ec92/attachment-0004.html>
More information about the RE-wrenches
mailing list