[RE-wrenches] Meter base minimum conductor size
Carl Adams
swingjunkie at gmail.com
Thu Feb 10 09:41:51 PST 2011
Thanks for the responses all. I think it's interesting that the same
type of lug is listed for smaller wire in one meter socket versus
another. I have used Mick's suggestion in the past and I will try out
the ferrule or barrel connector on our next project.
Cheers
Carl
On Wed, Feb 9, 2011 at 10:43 PM, Kent Osterberg <kent at coveoregon.com> wrote:
> Carl,
>
> You won't find the lugs being any different than the models that aren't
> listed for small wire, but using a meter base listed for the right wire is
> best.
> The Murray/Siemens 135-amp meter bases are listed for 14 AWG to 2/0
> http://cmsapps.sea.siemens.com/murray/murraycatalog/2008/08Murray_pdfs/08Murray_03/03_04-05.pdf
>
> Kent Osterberg
> Blue Mountain Solar
>
>
> Carl Adams wrote:
>>
>> Wrenches,
>>
>> We often use a conventional 100A meter base and analog meter as an
>> independent metering system for inverter output. These meters
>> typically have a minimum conductor size of #6 AWG. For smaller
>> systems the inverter output conductors are smaller than #6 AWG. We
>> have upsized the conductors to match the meter base requirement, but
>> this adds expense. I am looking for other suggestions for resolving
>> this.
>>
>> With Regards
>> Carl Adams
>> SunRock Solar
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list