[RE-wrenches] Meter base minimum conductor size
Kent Osterberg
kent at coveoregon.com
Wed Feb 9 19:43:32 PST 2011
Carl,
You won't find the lugs being any different than the models that aren't
listed for small wire, but using a meter base listed for the right wire
is best.
The Murray/Siemens 135-amp meter bases are listed for 14 AWG to 2/0
http://cmsapps.sea.siemens.com/murray/murraycatalog/2008/08Murray_pdfs/08Murray_03/03_04-05.pdf
Kent Osterberg
Blue Mountain Solar
Carl Adams wrote:
> Wrenches,
>
> We often use a conventional 100A meter base and analog meter as an
> independent metering system for inverter output. These meters
> typically have a minimum conductor size of #6 AWG. For smaller
> systems the inverter output conductors are smaller than #6 AWG. We
> have upsized the conductors to match the meter base requirement, but
> this adds expense. I am looking for other suggestions for resolving
> this.
>
> With Regards
> Carl Adams
> SunRock Solar