Re: [RE-wrenches] AGM battery charging, more details...."Until now"?.....
For proper VRLA battery charging, once it is full, you MUST reduce the voltage. It does not matter that you are opportunity charging. What if your turbine is making power 24/7? The voltage will still need to be reduced after a few hours or have a fixed voltage setting. I don't think you are ungrateful but again I encourage you to re-read this thread and the manufacturers instructions. It's all there.
Larry
----- Original Message -----
From: Hugh
To: RE-wrenches
Sent: Thursday, April 28, 2011 2:04 PM
Subject: Re: [RE-wrenches] AGM battery charging, more details
I am sorry if i seem ungrateful for the many useful ideas that have been voiced. I suppose I just like to try to oversimplify things. At present my over-simplification is to say that, for opportunity charging, the only thing that really matters is not to exceed the temperature-compensated absorption voltage. Until now I had imagined that it was dangerous to prolong the absorption voltage stage. But maybe float is not so important as making sure that the battery gets enough charge to prevent premature failure. By the time the charging current has dropped to the transition current level it is too low to do any damage and can be prolonged indefinitely (until wind and sun stop anyway). This would not work in a grid connected situation, but seems to fit for mine. I am sure you guys will point out if I have got this wrong.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110428/ebea5ab6/attachment-0003.html>
More information about the RE-wrenches
mailing list