[RE-wrenches] RV VS NEC

Dana dana at solarwork.com
Wed Feb 2 12:00:00 PST 2011


 

I have yet to find one RV that is even close to NEC. The company popup camper trips GFI breakers every time we try to plug into an outlet.  I have yet to discover what or how many appliances there are that are causing this issue.

 

Dana Orzel

Great Solar Works, Inc

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever believe anything, but seriously trust through action.

 

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Starlight Solar, Larry Crutcher
Sent: Wednesday, February 02, 2011 12:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Parallel wire runs to increase size

 

Dan and others, 

Thanks for the comments. The answer from Dan is what I was needing: 

"For two parallel runs of different sized conductors, add the circular mil area for both conductors, then using a wire table (such as a pocket guide), find the gauge closest to the total CMA to get the AWG equivalent."

 

Perhaps I should have explained that the PV system voltage is under 50 volts and that all conductors are bonded with terminal blocks at both ends. The current will distribute itself across the two conductors.

 

Just a side note for those concerned with the NEC and RV wiring: After years of wire installations in nearly every recreational vehicle made, I can assure you that not one RV is in total compliance with NEC. Some of the DC wiring performed by manufacturers is downright dangerous with long cable runs or many branch circuits with no circuit protection at all. Very scary. 

 