[RE-wrenches] 690.31(B) "within the photovoltaic array"
wirewiz at gmail.com
wirewiz at gmail.com
Tue Sep 6 12:43:47 PDT 2011
Wrenches,
I am installing Lumeta peel and stick modules (similar to laminates) on a
flat EPDM roof. No racking. NEC2008 690.31(B) says single conductor cable
listed and labeled as PV wire shall be permitted in exposed outdoor
locations..."within the array". 690.2 defines array as a mechanically
integrated assembly of modules or panels within a support structure...to
form a direct-current power producing unit. With the Lumeta's there is no
support structure. If you look at the diagram in the NEC 2008 (page 70-576)
it shows a box around the modules or panels and labels that box as the
"Array or photovoltaic power source".
My AHJ was at first not sure but then told me I had to install all the PV
wire in a listed raceway because the interconnects between the Lumeta's were
not within the array. But if you draw a box around all the Lumeta's it would
look like the array diagram that I referred to above.
Because of my roof layout, it would be much easier to install an unlisted
wire management system within the array rather than conduit which I will do
but in reading the NEC it just wasn't clear to me what "within the array"
means.
Any thoughts would be appreciated.
Thank you.
Larry Liesner
Design and Installations
Elektron Solar, LLC
16 Ketchum St.
Westport, CT 06880
203-557-3127 (office)
203-644-2404 (cell)
203-549-0977 (fax)
wirewiz at gmail.com
NABCEP Certified PV Installer (# 032611-184)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110906/6b5378ca/attachment-0002.html>
More information about the RE-wrenches
mailing list