[RE-wrenches] Aluminum conduit LBs
Drake Chamberlin
drake.chamberlin at redwoodalliance.org
Sun Aug 15 07:56:57 PDT 2010
Rather than use 3" pipe for the run, you could
use reducing bushings in a 3" LB and use it with a 2 1/2" conduit.
At 12:47 PM 8/14/2010, you wrote:
>The lesson was that even if, say, for a 2 ½
>conduit says three 350 MCMs are OK, that doesnt
>mean that a 2 ½ LB I was planning on using is rated for three 350s.
>
>For the first time ever I saw printed in the LB
>itself the specified max conduct size, in this case 4/0 for a 2 ½ LB.
>
>So for this short conduit run I upsized everything to 3.
>
>I looked at the Thomas and Betts spec sheet
>kindly supplied by Ratico on their LB offerings
>and there was no notation of max conductor sizes that I could find.
>
>marco
>
>Marco,
>I'm curious to know what you did after the
>"hard" lesson. Was it an issue of
>difficult/impossible installation, or an AHJ
>issue? It seems like the most straightforward
>solution in a situation like this is to replace
>your conduit bodies (LBs in this case) with a
>larger size, and then install reducers in order
>to leave the existing conduit runs intact. I'm
>looking at an upcoming installation where I
>would like to use 1-1/4" EMT, but will need
>1-1/2" conduit bodies to be ok with wire fill.
>
>-Hans
>
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org]
>On Behalf Of Marco Mangelsdorf
>Sent: Thursday, August 12, 2010 8:19 PM
>To: 'RE-wrenches'
>Subject: [RE-wrenches] Aluminum conduit LBs
>Anyone know where I could go to find out the max
>conductor sizes that threaded Al. LBs can handle?
>
>I learned the hard way that a conduit of X
>inches that can handle conductors of a certain
>size does not necessarily mean that a LB of the
>same diameter can handle the same size conductors.
>
>Thanks,
>marco
>
>
>No virus found in this incoming message.
>Checked by AVG - www.avg.com
>Version: 9.0.851 / Virus Database: 271.1.1/3067
>- Release Date: 08/12/10 08:34:00
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100815/605aaafd/attachment-0004.html>
More information about the RE-wrenches
mailing list