Rather than use 3" pipe for the run, you could use reducing bushings
in a 3" LB and use it with a 2 1/2" conduit. <br><br>
<br>
At 12:47 PM 8/14/2010, you wrote:<br><br>
<blockquote type=cite class=cite cite="">The lesson was that even if,
say, for a 2 ˝ “ conduit says three 350 MCMs are OK, that doesn’t mean
that a 2 ˝” LB I was planning on using is rated for three 350s.<br>
<br>
For the first time ever I saw printed in the LB itself the specified max
conduct size, in this case 4/0 for a 2 ˝” LB.<br>
<br>
So for this short conduit run I upsized everything to 3”.<br>
<br>
I looked at the Thomas and Betts spec sheet kindly supplied by Ratico on
their LB offerings and there was no notation of max conductor sizes that
I could find.<br>
<br>
marco <br>
<br>
Marco,<br>
I'm curious to know what you did after the "hard" lesson. Was
it an issue of difficult/impossible installation, or an AHJ issue? It
seems like the most straightforward solution in a situation like this is
to replace your conduit bodies (LBs in this case) with a larger size, and
then install reducers in order to leave the existing conduit runs intact.
I'm looking at an upcoming installation where I would like to use
1-1/4" EMT, but will need 1-1/2" conduit bodies to be ok with
wire fill. <br>
<br>
-Hans<br>
<br>
<hr>
<div align="center"></div>
<b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of
</b>Marco Mangelsdorf<br>
<b>Sent:</b> Thursday, August 12, 2010 8:19 PM<br>
<b>To:</b> 'RE-wrenches'<br>
<b>Subject:</b> [RE-wrenches] Aluminum conduit LBs<br>
Anyone know where I could go to find out the max conductor sizes that
threaded Al. LBs can handle?<br>
<br>
I learned the hard way that a conduit of X inches that can handle
conductors of a certain size does not necessarily mean that a LB of the
same diameter can handle the same size conductors.<br>
<br>
Thanks,<br>
marco<br>
<br><br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a><br>
Version: 9.0.851 / Virus Database: 271.1.1/3067 - Release Date: 08/12/10
08:34:00<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font size=1 color="#0000FF">TM
</font><font color="#0000FF">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>