[RE-wrenches] AC breakers used in DC applications
R Ray Walters
ray at solarray.com
Mon May 17 11:59:29 PDT 2010
I've also seen failures/ nuisance tripping due to loose connections at the breaker. The heat then wreaks havoc on the breaker internals.
R. Walters
ray at solarray.com
Solar Engineer
On May 17, 2010, at 8:23 AM, jay peltz wrote:
> HI Drake
>
> I don't know if this could apply to your situation, but I've seen the QO/QOU fail from debris getting into the breaker itself.
> Around here there are insects that deposit mud into small openings, like on those breakers.
> I've seen this cause the breakers to fail.
>
> jay
>
> peltz power
> On May 17, 2010, at 7:02 AM, Drake Chamberlin wrote:
>
>> The QO breaker I saw fail was a disconnect switch for an Air 303. The run from the battery bank was substantial, and the wire was number 10. At the time, I calculated the amperage available (I -V/R) and the short circuit current available was not close to the 5000 amp AIC of the breaker for its DC rating.
>>
>> At 06:13 PM 5/16/2010, you wrote:
>>> Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer. I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal tabs of the fuse holder (which had been greased with copper-laden Penetrox E) to their sockets. That indicates a fault current well north of 200,000 amps, quite possibly sseveral times that. A fire ensued, which triggered the gas protection system and fortunately resulted in almost no peripheral damage. It did cost about $10k to recharge and recertify the Inergen system. The inverter manufacturer was quite cagey on warranty replacement until they saw the photos - at which point a replacement miraculously arrived by overnight air.
>>>
>>>
>>>
>>> On May 15, 2010, at 9:43 , Drake Chamberlin wrote:
>>>
>>>> I did see a QO breaker fail to trip on a 24 volt DC system with only battery voltage behind it. It burned a #12 wire completely in two.
>>>>
>>>>
>>>>> The 48v is a max rating not a nominal rating.
>>>>> So yes only good for 12 and 24v systems.
>>>>>
>>>>> However with CBI breakers I don't understand why the need for QO for DC anymore?
>>>>>
>>>>> jay
>>>>>
>>>>> peltz power
>>>>> On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
>>>>
>>>> Drake Chamberlin
>>>> Athens Electric
>>>> OH License 44810
>>>> CO License 3773
>>>> NABCEP TM Certified PV Installer
>>>> Office - 740-448-7328
>>>> Mobile - 740-856-9648
>>>
>>> ___
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100517/3b6c525a/attachment-0004.html>
More information about the RE-wrenches
mailing list