Voltage is not the issue here, it is current, and battery fault currents can
be staggering - far more than one would ever encounter in a typical AC
system fed from a distribution transformer. I have seen a 200A Class T fail
to act on an 48V inverter fault which resulted in welding the metal tabs of
the fuse holder (which had been greased with copper-laden Penetrox E) to
their sockets. That indicates a fault current well north of 200,000 amps,
quite possibly sseveral times that. A fire ensued, which triggered the gas
protection system and fortunately resulted in almost no peripheral damage.
It did cost about $10k to recharge and recertify the Inergen system. The
inverter manufacturer was quite cagey on warranty replacement until they saw
the photos - at which point a replacement miraculously arrived by overnight
air.
On May 15, 2010, at 9:43 , Drake Chamberlin wrote:
I did see a QO breaker fail to trip on a 24 volt DC system with only battery
voltage behind it. It burned a #12 wire completely in two.
The 48v is a max rating not a nominal rating.
So yes only good for 12 and 24v systems.
However with CBI breakers I don't understand why the need for QO for DC
anymore?
jay
peltz power
On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100517/d83555c7/attachment-0004.html>
More information about the RE-wrenches
mailing list