[RE-wrenches] Supply Side Interconnections - Maximum Backfeed

Dave Click daveclick at fsec.ucf.edu
Thu Mar 4 17:34:41 PST 2010


Sometimes utilities will set a max too- here in Florida the 
investor-owned utilities have a rule that you take (DC at STC) x 0.85 to 
get the "AC equivalent" size of the array. That size then can't exceed 
90% of the service rating. Not sure if this is an issue in other states.

Scott McCalmont wrote:
> Going all the way up to the rating of the service might not be such a
> good idea. The utility may use smaller wires for the service drop than
> you would expect based on the ampacity tables in the NEC. Considering
> the example of a 400 A service:
>
> - PG&E (local utility) requires 350 kcmil Aluminum conductors.
> - Table 310.17 rates 350 kcmil Aluminum for 395 amps before temperature
> correction.
>
> With load diversity the smaller wires will be fine, but the output of a
> PV system is continuous. Running the output of a system sized at 400
> amps through the wires on a hot summer day could overload them.
>
> So... it depends.
>
> Scott
>
> Scott McCalmont, P.E.
> McCalmont Engineering
> San Jose, CA
> (408) 204-0318
>
>
> On Thu, Mar 4, 2010 at 3:02 PM, Michael Kelly <mike at solarflair.com
> <mailto:mike at solarflair.com>> wrote:
>
>     Kirpal,
>
>     That was always my interpretation as well.  So in the case of a 400A
>     service, I can backfeed 400A when utilizing a supply side
>     connection.  Others have thoughts on this?
>     - Mike
>
>     --
>     Michael Kelly
>     Project Manager / Project Engineer
>     NABCEP Certified Solar PV Installer ™
>
>     SolarFlair Energy, Inc.
>     11 Mayhew Street
>     Framingham, MA 01702
>     Direct Mobile: 617-899-9840
>     Main Phone: 508-293-4293
>     Main Fax: 508-293-4003
>     mike at solarflair.com <mailto:mike at solarflair.com>
>
>
>     On Thu, Mar 4, 2010 at 4:16 PM, Kirpal Khalsa <solarworks at gmail.com
>     <mailto:solarworks at gmail.com>> wrote:
>
>         Mike.....i may be wrong....but I think i am right....you are
>         limited by the wire size feeding the supply and/or  the
>         transformer size which supplies the service.....depending on the
>         physical location of the tap you may be limited by the enclosure
>         and the enclosure ratings as well
>         would love to hear any other ideas...
>         Cheers,
>         --
>         Sunny Regards,
>         Kirpal Khalsa
>
>         NABCEP Certified Solar PV Installer
>         Renewable Energy Systems
>         www.oregonsolarworks.com <http://www.oregonsolarworks.com/>
>         541-218-0201 m
>         541-592-3958 o
>
>
>         On Thu, Mar 4, 2010 at 12:50 PM, Michael Kelly
>         <mike at solarflair.com <mailto:mike at solarflair.com>> wrote:
>
>             Hi All,
>             Next to grounding, I find the calculation of the maximum
>             amount of backfeed current allowed in a supply side
>             connection to be the most vague issue in Article 690.  Let's
>             assume we have a 400A, 480/277 service in a commercial
>             building, a 400A main service disconnect, and the
>             jurisdiction is under NEC 2008.  What is the maximum
>             backfeed current allowed in a supply side connection?  The
>             only place the code points you to is 230.82(6), which is no
>             help, or to Article 705, which is no help either.  I know
>             that in the draft version of NEC 2011, there is
>             an expansion of 705.12(A) which states "* *Supply Side. An
>             electric power production source shall be permitted to be
>             connected to the supply side of the service disconnecting
>             means as permitted in 230.82(6). The sum of the ratings of
>             all overcurrent devices connected to power production
>             sources shall not exceed the rating of the service."  That
>             is a helpful sentence from the Code, but as it is in draft
>             form, what do we do under NEC 2008?  What have you used as a
>             maximum backfeed current for supply side connections?
>             Thanks,
>             Mike
>             --
>             Michael Kelly
>             Project Manager / Project Engineer
>             NABCEP Certified Solar PV Installer ™
>
>             SolarFlair Energy, Inc.
>             11 Mayhew Street
>             Framingham, MA 01702
>             Direct Mobile: 617-899-9840
>             Main Phone: 508-293-4293
>             Main Fax: 508-293-4003
>             mike at solarflair.com <mailto:mike at solarflair.com>
>
>             _______________________________________________
>             List sponsored by Home Power magazine
>
>             List Address: RE-wrenches at lists.re-wrenches.org
>             <mailto:RE-wrenches at lists.re-wrenches.org>
>
>             Options & settings:
>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>             List-Archive:
>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>             List rules & etiquette:
>             www.re-wrenches.org/etiquette.htm
>             <http://www.re-wrenches.org/etiquette.htm>
>
>             Check out participant bios:
>             www.members.re-wrenches.org
>             <http://www.members.re-wrenches.org/>
>
>
>
>
>
>         _______________________________________________
>         List sponsored by Home Power magazine
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>         <mailto:RE-wrenches at lists.re-wrenches.org>
>
>         Options & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         List-Archive:
>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>         List rules & etiquette:
>         www.re-wrenches.org/etiquette.htm
>         <http://www.re-wrenches.org/etiquette.htm>
>
>         Check out participant bios:
>         www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
>
>
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>



More information about the RE-wrenches mailing list