This is definitely deja vu all over again.  A 
system I designed, that disconnected 3 Sunny Boy 
inverters by having contactors on the load side 
of the transfer switch, had a problem.  When the 
contactors opened on generator exercise 
cycle,  the circuit breakers between the 
inverters and contactors tripped.  They did not 
trip every time, but randomly.  One or two would 
trip and the other would not.

After many hours of investigation and talking 
with SMA, no reason for this was ever found. The 
circuit apparently had no problem with nuisance 
tripping when the Sunny Boys were not 
producing.  We have theories, but tech support 
and other professionals do not think this should happen.

If you try this method, please let me know your results.