How do utilites go about adjusting the voltage at any given site? Adjustable
taps on the transformers on the poles? Do they have to go back to the
nearest sub-station? Re-arrange the distrubution of customers across
differenat areas of the grid.
I am in the dark here.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
Sent: Monday, December 20, 2010 8:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Low grid voltage fix
Hi Joel -
Have you tried getting PG&E out to check the line voltages? I believe they
need to be +/- 5% steady state (ANSI Range A) or possibly +/- 10% (Range
B) or they need to fix it. 105 V is way too low.
Here in the Bay Area I have found that PG&E is very receptive to resolving
line voltage issues. They normally have a tech out to the site within a few
hours after making a service call...