Insuating batteries does not have to be complicated. Several years ago, a Minnesota man (can't recall his name) who worked for the Jacobs brothers at their Wind Electric Company in the 1930's told me how he insulated his glass case Edison cells. He kept his battery bank outdoors on boards and covered with a tarp. Before the first snow, he would heap a big pile of loose hay on the tarp and then cover the whole hay pile and batteries with another tarp. Between winter storms he would lift the tarps and hay to check his batteries and add water if needed. He said he stored his potatoes and other root crops that didn't fit in his root cellar the same way. He and other old-timer in Massachusetts who also had Edison cells told me that they would dump out the electrolyte every 5 years and clean the jars and plates with plain water and add fresh electrolyte. The gentleman in Massachusetts bought his batteries from Mr. Edison in 1935 and was still using them in the early 1980s when he bought Arco ASI 16-2000 modules. Sensible people. Simpler times.

Joel Davidson
  ----- Original Message ----- 
  From: Dana 
  To: 'RE-wrenches' 
  Sent: Sunday, December 12, 2010 3:13 PM
  Subject: [RE-wrenches] To insulate a battery bank DEPENDS on a lot offactors.


  Great discussion and Thanks to all of you for the input.

   

  I thought of attempting a  wrap up of the various presentations but there are and always will be many variables in battery storage and insulation requirements. Here are my thoughts and a distillation from you all with respect to my high elevation climate in W. CO. - 6 months of winter and cool nights in summer [typically].

   

  Type of battery - Wet VS. Sealed batteries. : depends on size and usage of system and client choice.

   

  Climates – 4 season with 5-6 months of winter like conditions VS. a mild year round costal climate. : A long winter climate can seriously chill a poorly insulated bank and therefore reduce capacity when the bank get cold. I get more calls each Nov. from new to off grid folks with an under sized array and cold battery bank about reduced capacity.

   

  Does it cool off at night in the summer? VS. It is hot  24/7 for 4 months?

   

  Size of bank – Small VS. Large. : Smaller reacts more quickly to a cooling or heating trend VS. Larger react slowly.

   

  Ambient building temperature. – heated building VS. walled in shed/free standing battery box in a snowy scenario. : If I can put the bank on a temperature controlled radiant concrete slab I do so.

   

  Ability to sink the battery bank into the ground VS. not being able to do so. : installation & cost can be a challenge here.

   

  Powered venting VS.  convective venting ; Powered with a back draft damper seems to be a better option in winter climates. I have used the Zephyr Industries powered vent with backdraft damper for many years with great success.

   

  As mentioned batteries are an electrochemical unit that requires, like us, a narrow window for temperature to exist and operate efficiently. When working hardest, typically during winter, the recharge requirements are high and the hours of sunlight are low, therefore the temperature window is best on the warmer end of the range. 

   

  The time of year when power requirement can be lowest in summer, the usage is lower due to long days and lack of heating systems drawing them down over night, unless you are irrigating and perhaps a PV direct design would then be best.

   

  Thanks all.

   

   

  Dana Orzel

  Great Solar Works, Inc

  E - dana at solarwork.com

  V - 970.626.5253

  F - 970.626.4140

  C - 970.209.4076

  web - www.solarwork.com

   

  "Responsible Technologies for Responsible People since 1988"

  Do not ever belive anything, but seriously trust through action.

   

  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Joel Davidson
  Sent: Sunday, December 12, 2010 11:59 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] To insulate a battery bank -- sort of

   

  First of all, there is no one solution to battery selection, installation, operation, and maintenance. One size does not fit all. Allan and other wrenches with lots of battery experience have a good understanding about batteries in their regions for their customers.

   

  Second, insulation is used to control temperature change. Insulation slows both heat loss and gain. Large battery banks tend to change temperature slowly due to their mass and may not need insulation in your region or in a specific installation. The goal is to keep the battery bank at its optimum temperature. Cold batteries have reduced capacity. 40 F (4.4 C) is too cold for almost all RE system batteries. Hot batteries have shorter lives. Heat affects both battery chemistry and materials. For example, the plastic around Absolyte terminals cracks if their temperature is repeatedly 90 F (32.2 C) which can happen in an uninsulated battery area in the southwest U.S. So too hot or too cold is not good.

   

  Third, batteries need ventilation to safely remove hydrogen. Surprisingly, what most people consider a small amount of battery ventilation will suffice unless the battery bank is being charged excessively. For example, a PV system with eight 100 watt modules (rated 17.1 V, 5.88 A) and sixteen 6-volt batteries is wired for 24 volts DC. The required venting is 0.0135 x (5.88 x 4) x 12 = 3.81 CFM or 228.6 cubic feet per hour. Many, if not most, rooms are 8 feet in height with 2 air changes per hour. A room 8’ x 6’ x 6’ has 288 cubic feet volume and naturally vents 576 cubic feet per hour, almost 2.5 times the required 288.6 cubic feet per hour.

   

  In general, a battery area, room, box, etc. should be kept at 70 F (21.1 C), have good ventilation, no open flames (heater, gas water heater nearby?), no electrical sparks (automatic igniters, etc.?), easy to maintain and inspect, tidy, out of reach of non-authorized personnel, and have an up-to-date fire extinguisher handy.

   

  Batteries operate by electro-chemical process almost like living things. If they are too hot or too cold, they perform poorly and can die. If they are not fed properly (charged correctly), they will die. Interestingly, we use expressions like "die" and "end of life" to describe these non-living things. Most wrenches know people who party all weekend, don't eat well, forget to dress properly for the weather, and get sick. Likewise, if a battery bank is deeply discharged, not properly recharged, and too hot or too cold, it will perform poorly and die prematurely. You get the picture.

   

  Lastly, we have learned a lot about batteries in the 200 year since physicist, Allessandro Volta, developed the first cells. Unfortunately, a lot of battery myths exist. Explode myths (but not batteries) by asking the "5 whys". See http://en.wikipedia.org/wiki/5_Whys

   

  Joel Davidson

    ----- Original Message ----- 

    From: dan at foxfire-energy.com 

    To: RE-wrenches 

    Sent: Saturday, December 11, 2010 5:32 PM

    Subject: Re: [RE-wrenches] To insulate a battery bank -- sort of

     

    Ok, I'm a little reluctant to kick this critter much.. because I feel like I must be missing something here... but let me float this notion.. If we stuff flammable gas producing batteries in an enclosure (and proceed to button them up tighter than a bull's ass in fly season -- fan or no fan), Haven't we just created a Class I Division 1 location? (NEC 500.5).  then say we do rely on a $4. fan (OK -- $15.) to declassify as allowed in 500.5(A)fpn,  Wouldn't we still have a Class I Division 2 location? NEC 500.5(B)(2)(2)/(3). So my point is -- are fully enclosed battery boxes really worth the hassle? are they even A good idea? I can't seem to find where NFPA 70 "Requires" a battery enclosure.. 690 VIII  says you need to protect electrical connections (in dwellings) and kicks you back to 480, but makes no mention of "requiring" a battery enclosure.. 480.8 says basically that if you use racks or trays, they've got to hold up. 480.9 outlines ventilation and working space, but again doesn't "require" enclosures. (480.6 deals with Insulation of batteries.. But I'm thinking they're talking about electrical insulation)... But nowhere in the NEC have I found any mention of battery boxes or Enclosures being "Required"..  On the contrary, Seems to me they're suggesting that if by design you can provide for proper work space, adequate ventilation (both out and in) and protect the electrical connections, you're good as far as NEC is concerned.. In NFPA 70E, (Workplace Safety) 320.4 says batteries should be under lock and key (or require a tool for access), and that they be protected both physically and electrically.  also in NFPA 70E, 320.6 kicks around enclosure requirements some, but seems to focus more on protecting terminals and related equipment..  Now in OSHA 1926 (Subpart K), .441 seems to be where "required enclosures" originates, but again, it seems to be referring to commercial workplace safety... (i.e. also requires that "the charging apparatus be protected from damage by trucks" and "eye wash stations be provided within 25 feet" etc.).. I'll will tell you the majority of the failed / scummed out battery banks I've dealt with have been from poor ventilation, poor maintenance or defective / improperly designed or installed battery boxes.. If I can, one of the first remedy's I apply is to drill several large holes (and staple some kind of critter proofing over the holes from the inside). -or- if I can gracefully, I'll remove the sides altogether -- as long as the electrical connections are protected. also if I can, I try to find a way to route exhaust gases so they vent naturally -- so they don't rely solely on a vent fan... like maybe run 2" PVC up thru the roof -- inside the envelope of the house. at least try to make sure the fan is not competing with the furnace or exhaust systems... (like insure there's an adequate intake air supply for the whole house)...  as for protecting batteries from fluctuating temps.. the planet (some three feet down anyway) stays just over 48 degrees.. at least in these parts.. Just saying.. db


    Dan Brown
    Foxfire Energy Corp.
    Renewable Energy Systems
    (802)-483-2564
    www.Foxfire-Energy.com
    NABCEP #092907-44

     



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches at lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org