[RE-wrenches] GEC for Enphase inverters
Mark Frye
markf at berkeleysolar.com
Tue Sep 14 07:05:41 PDT 2010
I believe the AC GEC runs from; the point where the ungrounded current
carrying conductor is bonded to the enclosure of the service enterance
equipment; to the connection to the ground electrode system. Conductors that
run from the service enterance equipment, thru the premis to the Enphase are
bonding jumpers that are not required to be continuous.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, September 13, 2010 9:46 PM
To: RE-wrenches
Subject: [RE-wrenches] GEC for Enphase inverters
Friends:
According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be
continuous without splices unless they are irreversible. I am not clear
where this conductor starts and ends. Is it from the ground buss in a
sub-panel to the disconnect switch on the roof, or to each inverter?
Also, non-reversible splices need to be listed for use in grounding systems.
Any suggestions on make and model of splices so listed?
Any advise from those more experienced is much appreciated.
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com <http://millersolar.com/>
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100914/563bfc18/attachment-0003.html>
More information about the RE-wrenches
mailing list