size=2 face=Arial>I believe the AC GEC runs from; the point where the ungrounded 
current carrying conductor is bonded to the enclosure of the service enterance 
equipment; to the connection to the ground electrode system. Conductors that run 
from the service enterance equipment, thru the premis to the Enphase are bonding 
jumpers that are not required to be continuous.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=468365813-14092010><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN lang=en-us><FONT size=2 face=Arial>Mark 
Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley Solar 
Electric Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>303 
Redbud Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada 
City,  CA 95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>(530) 401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial> </FONT></SPAN> </DIV>
<DIV> </DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>William 
Miller<BR><B>Sent:</B> Monday, September 13, 2010 9:46 PM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> [RE-wrenches] GEC for Enphase 
inverters<BR></FONT><BR></DIV>
<DIV></DIV>Friends:<BR><BR>According to the 2005 NEC 250.64(C), the GEC for an 
AC system needs to be continuous without splices unless they are 
irreversible.  I am not clear where this conductor starts and ends.  
Is it from the ground buss in a sub-panel to the disconnect switch on the roof, 
or to each inverter?<BR><BR>Also, non-reversible splices need to be listed for 
use in grounding systems.  Any suggestions on make and model of splices so 
listed?<BR><BR>Any advise from those more experienced is much 
appreciated.<BR><BR>William Miller<BR><BR><X-SIGSEP>
<P></X-SIGSEP><FONT size=3><U>Please note new e-mail address and 
domain:<BR><BR></U>William Miller <BR>Miller Solar<BR>Voice 
:805-438-5600<BR>email: william@millersolar.com<BR><A 
href="http://millersolar.com/" 
eudora="autourl">http://millersolar.com<BR></A>License No. 
C-10-773985<BR></FONT></P></BODY></HTML>