The code does require the GEC to be continuous (250.64C), and I believe that the AC EGC for the Enphase metal inverter cases is in fact the same as the DC GEC since the point of system bonding on the DC side is inside the inverter. See art. 100 definitions:Grounding Electrode Conductor. A conductor used to
connect the system grounded conductor...to a point on the grounding electrode
system.
So this means that for Enphase systems the AC EGC (which is also the DC GEC) should be at minimum 8 awg (250.66) and continuous? Seems like it to me.
Rebekah Hren
--- On Tue, 9/14/10, Mark Frye <markf at berkeleysolar.com> wrote:
From: Mark Frye <markf at berkeleysolar.com>
Subject: Re: [RE-wrenches] GEC for Enphase inverters
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date: Tuesday, September 14, 2010, 10:05 AM
I believe the AC GEC runs from; the point where the ungrounded
current carrying conductor is bonded to the enclosure of the service enterance
equipment; to the connection to the ground electrode system. Conductors that run
from the service enterance equipment, thru the premis to the Enphase are bonding
jumpers that are not required to be continuous.
Mark
Frye
Berkeley Solar
Electric Systems
303
Redbud Way
Nevada
City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, September 13, 2010 9:46 PM
To:
RE-wrenches
Subject: [RE-wrenches] GEC for Enphase
inverters
Friends:
According to the 2005 NEC 250.64(C), the GEC for an
AC system needs to be continuous without splices unless they are
irreversible. I am not clear where this conductor starts and ends.
Is it from the ground buss in a sub-panel to the disconnect switch on the roof,
or to each inverter?
Also, non-reversible splices need to be listed for
use in grounding systems. Any suggestions on make and model of splices so
listed?
Any advise from those more experienced is much
appreciated.
William Miller
Please note new e-mail address and
domain:
William Miller
Miller Solar
Voice
:805-438-5600
email: william at millersolar.com
http://millersolar.com
License No.
C-10-773985
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100914/7f75820e/attachment-0003.html>
More information about the RE-wrenches
mailing list