Labeling For Grid-tie Solar Electric System
Great Solar Works, Inc., 970-626-5253
KNOPP SIGNS
Qty - 2, Color red
INTERACTIVE SYSTEM POINT OF INTERCONNECTION
Enphase Micro-Inverters [1] per module [17] Total
PHOTOVOLTAIC SYSTEM SOURCE
PV System Total Watts
3.910 KW
Maximum AC Output Operating Current
13.6 Amps
AC Operating Voltage
240 Volts
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty - 1, Color red
PHOTOVOLTAIC SYSTEM SOURCE
PV System Total Watts
3.910 KW
Maximum AC Output Operating Current
13.6 Amps
AC Operating Voltage
240 Volts
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty - 1, Color red
PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT
WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.
TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED
IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE
NORMALLY GROUNDED CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty -1, Color Yellow
PHOTOVOLTAIC SYSTEM CONNECTED
THE AC PV DISCONNECT IS LOCATED
Next to Meter on South Wall
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Thanks, Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
Responsible Technologies for Responsible People since 1988"
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100517/5635e85e/attachment-0003.html>
More information about the RE-wrenches
mailing list