[RE-wrenches] AC breakers used in DC applications
Kurt Albershardt
info at es-ee.com
Sun May 16 15:30:41 PDT 2010
Small (QO or Airpax-type) breakers in a distribution bank should be front ended with a suitable DC master breaker or fuse that has the capability to interrupt the available fault current. Ideally, the series combination should be rated but at a minimum, a coordination study should be undertaken.
I like to have primary protection on each string, as close to the battery as possible - preferably bolted to the battery terminal. Cable limiters are nice, but a TPL style fuse is easier to get.
On May 16, 2010, at 16:13 , Kurt Albershardt wrote:
> Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer. I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal tabs of the fuse holder (which had been greased with copper-laden Penetrox E) to their sockets. That indicates a fault current well north of 200,000 amps, quite possibly several times that. A fire ensued, which triggered the gas protection system and fortunately resulted in almost no peripheral damage. It did cost about $10k to recharge and recertify the Inergen system. The inverter manufacturer was quite cagey on warranty replacement until they saw the photos - at which point a replacement miraculously arrived by overnight air.
>
>
>
> On May 15, 2010, at 9:43 , Drake Chamberlin wrote:
>
>> I did see a QO breaker fail to trip on a 24 volt DC system with only battery voltage behind it. It burned a #12 wire completely in two.
>>
>>
>>> The 48v is a max rating not a nominal rating.
>>> So yes only good for 12 and 24v systems.
>>>
>>> However with CBI breakers I don't understand why the need for QO for DC anymore?
>>>
>>> jay
>>>
>>> peltz power
>>> On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
>> Drake Chamberlin
>> Athens Electric
>> OH License 44810
>> CO License 3773
>> NABCEP TM Certified PV Installer
>> Office - 740-448-7328
>> Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100516/9fc584ea/attachment-0003.html>
More information about the RE-wrenches
mailing list