[RE-wrenches] AC breakers used in DC applications
Kurt Albershardt
info at es-ee.com
Sun May 16 15:13:42 PDT 2010
Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer. I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal tabs of the fuse holder (which had been greased with copper-laden Penetrox E) to their sockets. That indicates a fault current well north of 200,000 amps, quite possibly sseveral times that. A fire ensued, which triggered the gas protection system and fortunately resulted in almost no peripheral damage. It did cost about $10k to recharge and recertify the Inergen system. The inverter manufacturer was quite cagey on warranty replacement until they saw the photos - at which point a replacement miraculously arrived by overnight air.
On May 15, 2010, at 9:43 , Drake Chamberlin wrote:
> I did see a QO breaker fail to trip on a 24 volt DC system with only battery voltage behind it. It burned a #12 wire completely in two.
>
>
>> The 48v is a max rating not a nominal rating.
>> So yes only good for 12 and 24v systems.
>>
>> However with CBI breakers I don't understand why the need for QO for DC anymore?
>>
>> jay
>>
>> peltz power
>> On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
> Drake Chamberlin
> Athens Electric
> OH License 44810
> CO License 3773
> NABCEP TM Certified PV Installer
> Office - 740-448-7328
> Mobile - 740-856-9648
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100516/69329d10/attachment-0003.html>
More information about the RE-wrenches
mailing list