[RE-wrenches] AC breakers used in DC applications

Kurt Albershardt info at es-ee.com
Sun May 16 15:13:42 PDT 2010


Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer.  I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal tabs of the fuse holder (which had been greased with copper-laden Penetrox E) to their sockets.  That indicates a fault current well north of 200,000 amps, quite possibly sseveral times that.   A fire ensued, which triggered the gas protection system and fortunately resulted in almost no peripheral damage.  It did cost about $10k to recharge and recertify the Inergen system.  The inverter manufacturer was quite cagey on warranty replacement until they saw the photos - at which point a replacement miraculously arrived by overnight air.



On May 15, 2010, at 9:43 , Drake Chamberlin wrote:

> I did see a QO breaker fail to trip on a 24 volt DC system with only battery voltage behind it.  It burned a #12 wire completely in two.  
> 
> 
>> The 48v is a max rating not a nominal rating.
>> So yes only good for 12 and 24v systems.
>> 
>> However with CBI breakers I don't understand why the need for QO for DC anymore?
>> 
>> jay
>> 
>> peltz power
>> On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
> Drake Chamberlin
> Athens Electric
> OH License 44810
> CO License 3773
> NABCEP TM  Certified PV Installer 
> Office - 740-448-7328
> Mobile - 740-856-9648
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100516/69329d10/attachment-0003.html>


More information about the RE-wrenches mailing list