[RE-wrenches] Off-Grid Sizing Case
jay peltz
jay at asis.com
Thu Dec 3 11:07:52 PST 2009
Hi Mark,
I'd install as much PV as I could afford, a MPPT controller and a battery capacity meter to keep an eye on things.
And if they are still looking to throw money around then a new generator as Allan suggested.
jay
peltz power
On Dec 3, 2009, at 9:22 AM, Mark Frye wrote:
> Folks,
>
> I have a customer with a 3 year old system in northern CA:
>
> 8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V
> 2 - DR2424 120/240V series
> 4 - EC-120-GL
> 1 - C40 CC
> 1 - 5000W, old portable gas gen
>
> The problem is increased gen runtime probally due to chronic undercharging.
>
> Based on estimated consumption in the home, I think he needs about 2X the PV to meet the energy production needs in the summer (5 kWH/day)(30% DOD/day). But in order to get C10 charging during the summer he would need 5X the PV?
>
> Money is and issue. So what should I recommend:
>
> 1 - Increase PV 4X to 5X, add MPPT controller to get to a PV based system with gen support
> 2 - Get a 3K to 5K propane gen and and run as a gen based system with PV support
> 3 -?
>
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City, CA 95959
> (530) 401-8024
> www.berkeleysolar.com
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091203/5ee63e7b/attachment-0004.html>
More information about the RE-wrenches
mailing list