[RE-wrenches] Mobile Solar power Center
Starlight Solar, Yuma, AZ
larry at starlightsolar.com
Mon Jan 19 13:06:05 PST 2009
Peter,
We use ANL type fuses (see here) in mobile applications for circuits
like converters, generator starters and other heavy distribution
circuits up to 300 amp. For large inverters with 2/0 and above cable
we recommend Class T fusing.
The Prosine 1000 should be protected with a 150 amp fuse (see table 4
of the manual). For simple short circuit protection the ANL should
work fine. It has an interrupt rating of about 2700 amperes and up to
80 Vdc. I am not positive about the legality. The way I understand it,
SAE makes standards and NEC makes no rules for 12 volt mobile systems.
Larry Crutcher
Starlight Solar
11279 S. Glenwood Ave #11114
Yuma, AZ 85367
(928) 941-1660
larry at starlightsolar.com
www.starlightsolar.com
Retail Store: 2998 Shari, Yuma, AZ
Renewable Energy Products, Service and Installation
On Jan 19, 2009, at 9:49 AM, Peter Parrish wrote:
> We are designing a "Mobile Solar Power Center" to power Eco-Events
> and the
> like in Southern California. We will have 1,600 Wp of solar panels,
> 6 kWh of
> 24 V AGM battery backup and a 1kW / 120 VAC inverter. I am designing
> the
> system from scratch, and I wondered if anyone else out there has put
> together a similar system and was inclined to share notes. When I'm
> finished
> I'd be glad to do the same.
>
> One stumbling block I have right now, is to find a DC rated 70A in-
> line
> fuse, to put between the battery bank and the input to the inverter.
> 70A may
> seem an odd value, but it is the best choice for the surge rating of
> the
> inverter I'll be using (Xantrex Prosine 1000). Does anyone have a
> source for
> DC-rated in-line fuses?
>
> Thanks in advance, -Peter
>
> Peter T. Parrish, President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090119/d10fb1a6/attachment-0004.html>
More information about the RE-wrenches
mailing list