<html><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><div>Peter,</div><div><br></div><div>We use ANL type fuses <a href="http://cgi.ebay.com/Inverter-Solar-RV-Motorhome-Fuse-Holder-and-Fuse-ANL_W0QQitemZ140182375295QQcmdZViewItemQQptZElectrical_Solar_US?hash=item140182375295&_trksid=p4634.c0.m14.l1262">(see here)</a> in mobile applications for circuits like converters, generator starters and other heavy distribution circuits up to 300 amp. For large inverters with 2/0 and above cable we recommend Class T fusing. </div><div><br></div><div>The Prosine 1000 should be protected with a 150 amp fuse (see table 4 of the manual). For simple short circuit protection the ANL should work fine. It has an interrupt rating of about 2700 amperes and up to 80 Vdc. I am not positive about the legality. The way I understand it, SAE makes standards and NEC makes no rules for 12 volt mobile systems.</div><div apple-content-edited="true"><div><div><div><div><div><br></div><div>Larry Crutcher</div><div>Starlight Solar</div><div>11279 S. Glenwood Ave #11114</div><div>Yuma, AZ 85367</div><div>(928) 941-1660</div><div><br></div><div><a href="mailto:larry@starlightsolar.com">larry@starlightsolar.com</a></div><div><a href="http://www.starlightsolar.com">www.starlightsolar.com</a> </div></div><div><br></div><div>Retail Store: 2998 Shari, Yuma, AZ</div><div><br></div>Renewable Energy Products, Service and Installation</div><div><br></div><div><br></div></div><br></div><br> </div><br><div><div>On Jan 19, 2009, at 9:49 AM, Peter Parrish wrote:</div><br><blockquote type="cite"><div>We are designing a "Mobile Solar Power Center" to power Eco-Events and the<br>like in Southern California. We will have 1,600 Wp of solar panels, 6 kWh of<br>24 V AGM battery backup and a 1kW / 120 VAC inverter. I am designing the<br>system from scratch, and I wondered if anyone else out there has put<br>together a similar system and was inclined to share notes. When I'm finished<br>I'd be glad to do the same.<br><br>One stumbling block I have right now, is to find a DC rated 70A in-line<br>fuse, to put between the battery bank and the input to the inverter. 70A may<br>seem an odd value, but it is the best choice for the surge rating of the<br>inverter I'll be using (Xantrex Prosine 1000). Does anyone have a source for<br>DC-rated in-line fuses? <br><br>Thanks in advance, -Peter<br><br>Peter T. Parrish, President<br>California Solar Engineering, Inc.<br>820 Cynthia Ave., Los Angeles, CA 90065<br>Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885<br>CA Lic. 854779, NABCEP Cert. 031806-26<br><a href="mailto:peter.parrish@calsolareng.com">peter.parrish@calsolareng.com</a> <br><br><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br><br></div></blockquote></div><br></body></html>