[RE-wrenches] concord batteries, EQUALIZE Them!

Travis Creswell tcreswell at ozarkenergyservices.com
Tue Dec 1 10:18:41 PST 2009


I wish I had more time to detail this but alas..with that many strings I'm
pretty sure most of the batteries in this bank are toast.  I would do a
quick and dirty pass/fail test on each battery with a hand held 100 amp load
tester.  I paid $20 for mine at Harbor Freight and it's one of my most used
meters.  Within just a second or two you'll know because some batteries will
fall on their face and I bet they are goners.  

 

Before you unhook all the batteries for the load test park the inverter the
inverter bulk and float voltages at ~58v so it doesn't taper off.  Then go
through and check each battery.  I suspect you'll find some at 11 and some
15 or higher all within the same string (string volts will always add up to
58 of course).  Again I bet high ones are toast and you might be able to
save to low ones.

 

Then you can patch together one or two strings in effort to get the system
in some sort of operational state while the owner digests that his $12,000
($300 each x 40) battery is toast but even if you could fix it, it's just a
bad band-aid and he needs to pony up another $8k-$12k for a real battery
bank.

 

Gotta go, good luck!

 

Travis Creswell

Ozark Energy Services

 

 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar
Sent: Tuesday, December 01, 2009 11:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] concord batteries, EQUALIZE Them!

 

If the 180 watt panel will provide enough current to run the recovery
process, then give it a try. What I expect is that your current will vary
throughout the day. Not sure if this is a critical point or if it will just
prolong the process. Pay attention to the temperature. I use a laser temp
probe on the terminals every 30 minutes to verify.

 

Another thing to monitor is the current. It will probably start very low and
build over time due to high resistance from sulfated plates. During this
time the voltage might get really high and then lower some. Don't worry
about the voltage. After a while the current will begin to drop. This means
the recovery process is working. 

 

I just realized that this battery bank must be 4 in series and ten parallel
strings. This is a horrible design that can never work right without
extensive monthly maintenance. The strings with higher resistance will not
be charged properly. Because of this, many strings will be undercharged
every day. EVERY day! So even if you recover these batteries, someone will
need to test and equalize at least every month. I really want to stress this
point as multiple parallel batteries are the ruin and waste of many
thousands of tons of batteries each year. I never design for more than two
strings in parallel. Do this and be happy.

 

Larry Crutcher

www.starlightsolar.com

larry at starlightsolar.com

(928) 941-1660

 

Retail Store & Shipping 

2998 Shari Ave.

Yuma, AZ 85365

 

Mailing address

11881 South Fortuna Road; #210

Yuma, AZ 85367

 

Renewable Energy Systems Sales, Service, Installations

 

On Dec 1, 2009, at 6:00 AM, Conrad Geyser wrote:





Thanks for the amazing responses everyone!

 

Larry, it sound as though the parameters below are a perfect match for your
average ~180 watt PV module in December sunlight wired back through a diode
to a test battery inside?  Does it matter if the process get's interrupted
by a few nights / cloudy days?  Do you have a preferred test approach?

 

Yeah, this bank represents a huge amount of resources; I want to make sure
it can't be saved.

 

Conrad

Cotuit Solar

 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar
Sent: Monday, November 30, 2009 11:17 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] concord batteries, EQUALIZE Them!

 

Conrad,

 

We have sold many Concord (Lifeline, Sun Xtender...) batteries over the
years. They are the best and half of our battery sales are Deka and Concord
AGM's.

 

When our mobile customers abuse their AGM batteries, I use an equalization
process that has a constant current and no voltage limit to restore them. I
am sure you have heard that you should never equalize an AMG battery. This
is not true but the process must be tightly controlled. I have done it many
times and the result is always to recover some or most capacity. 

 

Do one battery at a time.

1. Battery temp: 77 degrees (+/-5) and stable

2. Apply charge current limited to 5% of the 20hr rate. eg. 220 AH will be
11 amps. Do not regulate voltage!

3. Monitor temperature and voltage.

4(a) If temperature reaches 130F, stop the process. Start again when the
battery temperature has been lowered to room temperature.

4(b) When voltage reaches 2.6 vpc, continue charging for 4 hours. Voltage
may reach 3 vpc!!  Follow 4(a) about temp.

5. After this process, perform a capacity test. 

 

This has worked for me with chronically undercharged AGM's of all types. I
have never had one vent or go into thermal run away. At the price of these
batteries, it is worth the time to try if you have the power source and
time.

 

For reference this process is outlined in the Lifeline Technical manual,
page 20. http://www.lifelinebatteries.com/manual.pdf

 

Larry Crutcher

www.starlightsolar.com

larry at starlightsolar.com

(928) 941-1660

 

On Nov 29, 2009, at 6:48 PM, Conrad Geyser wrote:






In the vein of us on grid folks who's heads spin when the off grid folks
start talking about charge programming and gen set start up parameters.

 

I am servicing an orphaned 48 V off grid system that is only 1 1/2 years
old, with 40 Concorde Sun Extender batteries, which are for the most part,
shot (about half of them under 10V after a generator EQ charge).  I'm sure
the batteries have been abused at least after the point that someone lowered
the generator start voltage to 40V.  We're still doing fact finding on the
charge parameters for the PV and wind, but I'm wondering if there is anyone
that has an opinion on the Concorde batteries.

 

And at least at this point, I'm glad I had to study for some off grid
questions on the NABCEP test, not to mention the conversations on this list.
: >

 

Conrad

Cotuit Solar

 

 

 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bob-O
Schultze
Sent: Wednesday, November 25, 2009 9:59 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Nabcep - grid tie---Off grid

 

William,

Nice to meet you -however briefly- at the Solar Zoo in Anaheim.

If you don't see the value in being NABCEP certified, then you shouldn't
bother with it. If your state- as more than a few have- decides to recognize
it in some way that affects your pocket, then you'll likely change your mind
PDQ. I've personally gotten one or two jobs that I know about because I was
Certified and the other bidder was not, but our bids were very close in
price. Low-ballers, like head lice, are just a nasty fact of life.

While I generally agree with you on your point #2, it varies a lot state to
state. I'm licensed in CA and OR. While I understand the rules in CA are
changing, enforcement is, and has always been, a joke. In OR, you need a
4000 hour apprenticeship AND 256 hours of general electrical classroom time
to get a Renewable Energy license. A general journeyman license is twice
that. I've had inspectors come to our job site and check that everyone is
licensed. In OR, you don't lay hands on a wire without a license. Ever hear
of the like in CA? Maybe in the big cities, but nowhere else.

We're totally on the same page about the IBEW. If you understand that their
goal is total domination of the electrical trade everywhere, a lot of how
they operate makes sense. I'm a pro-Union kinda guy as a rule, but, like
religion, too much of a thing is way worse than none.

As to experience with EMT and the like, again it varies state to state and
certainly region to region. In this neck of the woods, if you can't bend an
offset or saddle bend, you are either a new apprentice or unemployed.

Best, Bob-O

 

On Nov 24, 2009, at 11:48 PM, William Miller wrote:

 

Friends:

I'd like to make two brief points on the training/NABCEP debate:

1. If I thought NABCEP certification would get me one more job I'd normally
lose to a low-ball bidder, I'd be inclined to sit for the test, but it
won't.

2. Most solar electric installers could not be considered electricians.
Until they learn the trade, they are not qualified to install the most basic
grid tie system.  Conversely, many electricians with the most basic
electrical skills think they know all that needs to be known to design and
install solar-electric.  Wrong again.

I don't support the IBEW concept of taking over the solar industry by force,
but I do respect their concept of actually encouraging well rounded
electrician's skills.  How many solar installers can actually lay an offset
into a stick of EMT?  Not many.  Most are glorified stereo installers,
plugging and praying.

Respectfully,

William Miller

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20091201/eca952ee/attachment-0003.html>


More information about the RE-wrenches mailing list