At 10:08 -0500 12/11/09, Drake Chamberlin wrote:
>
>
>Using a 3 to 2 prong adaptor might be the best solution where code
>rigidity is not the norm.
As I understand it, this removes the grounding wire that linked the
genset to the house. If the neutral wire comes loose, then you are
almost guaranteed to have a lethal voltage between the generator
frame and house ground. That doesn't seem likely to be the safest
solution although it might be the simplest to install.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk