[RE-wrenches] XW6048 parts problem
Mark.Edmunds at ca.schneider-electric.com
Mark.Edmunds at ca.schneider-electric.com
Mon Sep 21 11:06:21 PDT 2009
Hi Drake,
I had not heard about this battery incident you mention below...do you
have any other details? So far there has not been any record of battery
problems on the XW that I know of and we obviously would like to hear if
there is something we should be looking in to.
Hi Peter - as far as I recall we resolved the issue you mention below back
in January, and from our records the customer has been happy with the
results. It was a pretty unusual condition that our tech support team had
not seen before, and it took the senior designer of the XW product to
finally be able to understand what was going on. A learning "opportunity"
for all.
Cheers,
Mark
_____________________________________________________________________________________
Mark Edmunds | Schneider Electric | Renewable Energies Business |
CANADA | Senior Director, Engineering
Phone: +1-604-422-2609 | Mobile: +1-604-613-3285
Email: mark.edmunds at ca.schneider-electric.com | Site: www.xantrex.com |
Address: 8999 Nelson Way, Burnaby, BC V5A 4B5, CANADA
*** Please consider the environment before printing this e-mail
From:
Drake Chamberlin <drake.chamberlin at redwoodalliance.org>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
09/20/2009 05:10 PM
Subject:
Re: [RE-wrenches] XW6048 parts problem
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Hi Peter,
Do you need the extra fan? The VFX has an internal fan. Are there a lot
of heavy loads that push the limits of the Outback? If not, take out the
fan or swap it for a cover with no fan. Many VFX inverters didn't come
with cover fans. I don't know if they are standard now, or not.
Or, have the fan go on whenever the direct grid tie inverter is being
called on to charge batteries instead of feed the grid. If loads are not
real heavy, battery charging, by back feeding the AC Out, may be the time
when the fan is needed the most.
Before inverters started controlling generators, we used a device called
the Simple Switch, which was a voltage controlled contact. (We'd use it
with a GenWiz). I'm not sure what is out there these days. You could use
the Atkinson GSCM, generator start module, which senses the voltage. If
you need this solution, I'd call AEE.
Thanks for the heads up on the Xantrex. I just heard another horror story
about the Xantrex 6024 system. According to the installer, the owner shut
off an AC switch and the array cooked a bank of Surrette 25CS 25 PS
batteries. I don't know the new Xantrex line and don't understand how
this could happen. Is this really possible?
-Drake
At 06:43 PM 9/20/2009, you wrote:
Hi Drake (and everyone else interested in this thread),
Armed with the information from my esteemed colleagues, we went ahead and
purchased a SunWise ?Solar Ready-Grid Tie Battery System?, a SRB3.6 to be
exact. The heart of the system is a GVFX3648. I ordered it without the
Charge controller and purchased a SB3000 and 3150 Wdc of PV to go with it.
I also purchased a Grainger 2P2T relay with a 12 V coil in a NC
configuration (to disconnect the SB when the batteries are fully charged
in off-grid mode) and an Outback PSX-240 to transform the 240 Vac to 120
Vac (in order to interface with the GVFX3648.
When we looked into hooking the relay up to the AUX-OUT of the GVFX3648,
we discovered that it was already dedicated to the fan?
So it looks like we will need to put something together to sense the
battery voltage and energize the relay coil, when we exceed the threshold.
Any recommendations for a add-on HVD? And exactly what threshold voltage
should we use for 8ea 6V 305 Ah (C/24) AGM batteries?
And for Drake: I gravitated away from Xantrex because of a very
unsatisfactory experience with a XW6048. The system failed to work
properly and Xantrex ?hemmed and hawed? for over six months. Bottom line:
we made six service calls, two firmware upgrades and probably two dozen
calls to largely clueless group tech supporters. Through it all, I lost
the customer?s confidence and he chose another integrator to do a follow
on commercial project. The last part of course was the worst part of the
experience.
- Peter
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090921/adaa53b1/attachment-0003.html>
More information about the RE-wrenches
mailing list