[RE-wrenches] XW6048 parts problem
Drake Chamberlin
drake.chamberlin at redwoodalliance.org
Mon Sep 21 13:49:58 PDT 2009
Hi Mark,
I will talk to the installer to get more details.
At 02:06 PM 9/21/2009, you wrote:
>Hi Drake,
>
>I had not heard about this battery incident you
>mention below...do you have any other details?
>So far there has not been any record of battery
>problems on the XW that I know of and we
>obviously would like to hear if there is something we should be looking in to.
>
>Hi Peter - as far as I recall we resolved the
>issue you mention below back in January, and
>from our records the customer has been happy
>with the results. It was a pretty unusual
>condition that our tech support team had not
>seen before, and it took the senior designer of
>the XW product to finally be able to understand
>what was going on. A learning "opportunity" for all.
>
>Cheers,
>
>Mark
>
>_____________________________________________________________________________________
>
>
>Mark Edmunds | Schneider
>Electric | Renewable Energies
>Business | CANADA | Senior Director, Engineering
>Phone: +1-604-422-2609 | Mobile: +1-604-613-3285
>Email:
><mailto:mark.edmunds at ca.schneider-electric.com>mark.edmunds at ca.schneider-electric.com
>| Site: www.xantrex.com | Address: 8999
>Nelson Way, Burnaby, BC V5A 4B5, CANADA
>
>*** Please consider the environment before printing this e-mail
>
>
>
>From: Drake Chamberlin <drake.chamberlin at redwoodalliance.org>
>To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>Date: 09/20/2009 05:10 PM
>Subject: Re: [RE-wrenches] XW6048 parts problem
>Sent by: re-wrenches-bounces at lists.re-wrenches.org
>
>
>
>
>Hi Peter,
>
>Do you need the extra fan? The VFX has an
>internal fan. Are there a lot of heavy loads
>that push the limits of the Outback? If not,
>take out the fan or swap it for a cover with no
>fan. Many VFX inverters didn't come with cover
>fans. I don't know if they are standard now, or not.
>
>Or, have the fan go on whenever the direct grid
>tie inverter is being called on to charge
>batteries instead of feed the grid. If loads
>are not real heavy, battery charging, by back
>feeding the AC Out, may be the time when the fan is needed the most.
>
>Before inverters started controlling generators,
>we used a device called the Simple Switch, which
>was a voltage controlled contact. (We'd use it
>with a GenWiz). I'm not sure what is out there
>these days. You could use the Atkinson GSCM,
>generator start module, which senses the
>voltage. If you need this solution, I'd call AEE.
>
>Thanks for the heads up on the Xantrex. I just
>heard another horror story about the Xantrex
>6024 system. According to the installer, the
>owner shut off an AC switch and the array cooked
>a bank of Surrette 25CS 25 PS batteries. I
>don't know the new Xantrex line and don't
>understand how this could happen. Is this really possible?
>
>-Drake
>
>At 06:43 PM 9/20/2009, you wrote:
>Hi Drake (and everyone else interested in this thread),
>
>Armed with the information from my esteemed
>colleagues, we went ahead and purchased a
>SunWise Solar Ready-Grid Tie Battery System, a
>SRB3.6 to be exact. The heart of the system is a
>GVFX3648. I ordered it without the Charge
>controller and purchased a SB3000 and 3150 Wdc of PV to go with it.
>
>I also purchased a Grainger 2P2T relay with a 12
>V coil in a NC configuration (to disconnect the
>SB when the batteries are fully charged in
>off-grid mode) and an Outback PSX-240 to
>transform the 240 Vac to 120 Vac (in order to interface with the GVFX3648.
>
>When we looked into hooking the relay up to the
>AUX-OUT of the GVFX3648, we discovered that it
>was already dedicated to the fan
>
>So it looks like we will need to put something
>together to sense the battery voltage and
>energize the relay coil, when we exceed the
>threshold. Any recommendations for a add-on HVD?
>And exactly what threshold voltage should we use
>for 8ea 6V 305 Ah (C/24) AGM batteries?
>
>And for Drake: I gravitated away from Xantrex
>because of a very unsatisfactory experience with
>a XW6048. The system failed to work properly and
>Xantrex hemmed and hawed for over six months.
>Bottom line: we made six service calls, two
>firmware upgrades and probably two dozen calls
>to largely clueless group tech supporters.
>Through it all, I lost the customers confidence
>and he chose another integrator to do a follow
>on commercial project. The last part of course
>was the worst part of the experience.
>
>- Peter
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090921/9cbfa8eb/attachment-0004.html>
More information about the RE-wrenches
mailing list