[RE-wrenches] Micro Hydro MPPT
Jeff Clearwater, Village Power Design
jeffc at villagepower.com
Sun Oct 19 10:25:42 PDT 2008
Hi Carl,
Depends on what kind of microhydro output you are talking.
We have installed two systems now with a HiPower 3-phase inductive
Alt output voltage clamped and rectified straight into a SMA standard
SunnyBoy (with blessings from SMA). As long as you don't go over 600
VDC the warranty applies and the MPPT locks in nicely.
I don't have experience with going direct DC like from a PM motor
though - probably would work but maybe others have some experience
with this?
Best,
Jeff
>Hullo again,
>
>Can someone comment on the use of SMA Windyboy with microhydro.
>
>I understand that the Windyboy MPPT table is specific to a Wind Turbine.
>
>Does this matter? Is the MPPT table critical in the case of a hydro
>with little variation of output ??
>
>Thanks for your help.
>
>Carl Emerson
>Free Power
>Auckland NZ
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
--
~~~~~~~~~~~~~
Jeff Clearwater
Senior Design Engineer
NABCEP (tm) Certified Solar PV Installer
http://www.nabcep.org/
Village Power Design
Turnkey Solar Design & Installation for the Commercial Sector
http://www.villagepower.com
gosolar at villagepower.com
Voice: 413-259-3776
Fax: 413-825-0703
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081019/c77792ae/attachment-0004.html>
More information about the RE-wrenches
mailing list