SW4048 with GTI- suitable for off-grid? [RE-wrenches]
William Miller
wrmiller at charter.net
Tue Jul 1 11:36:46 PDT 2008
<x-flowed>
Mark:
Thank you very much!
William Miller
At 11:29 AM 7/1/2008, you wrote:
>Hi William,
>
>The GTI units are only needed if the SW's are to be used in Sell mode.
>In your case the GTI's do not need to be installed, and the inverters
>can be used as-is without problem. Even in an on grid application, if
>the inverters are not in sell mode, the GTIs don't need to be connected.
>
>
>Just FYI, if dealing with a system that already has the GTIs connected,
>the only requirement is to remove the 9-pin ribbon cable from the GTI.
>Power conductors do not need to be removed/rerouted.
>
>Cheers,
>
>Mark
>
>
>Mark Edmunds
>Xantrex Technology Inc.
- - - -