Darryl Thayer
daryl_solar at yahoo.com
Wed Jan 16 15:35:14 PST 2008
Sorry to post twice, I took a look at meter diagram.
the 4 jaw meter has a voltage coil and two current
coils to determine the power. The Sunny Boy 5000US
does not send power on the neutral I believe. So the
4 jaw should work fine. The 5 Jaw meter form 12S has
two voltage coils and two current coils. So it can
acuracly measure the power on a (two legs) of a three
phase power. The 12S meter is not very expensive ,and
Austin Inc (austininc.com) has low cost 5 jaw meters
an meter sockets.
hope this is helpful
Darryl
--- Nicholas Ponzio <nponzio at buildingenergyus.com>
wrote:
> Wrenches,
>
> We're installing a Sunny Boy 5000US in a commercial
> building with
> 3-phase 208 (L1, L2, L3, N). The output of the SB
> will only be
> 1-phase, 208 (L1, L2, N). How do I meter this? Will
> a standard 240V
> kwh meter be accurate in this application or do I
> need a 3-phase
> meter?
>
> Thanks in advance for any input.
> -Nik
>
____________________________________________________________________________________
Never miss a thing. Make Yahoo your home page.
http://www.yahoo.com/r/hs
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list