[RE-wrenches] load side taps and NEC 240.21

Mark Frye markf at berkeleysolar.com
Fri Dec 5 17:10:08 PST 2008


120% allowance is only "..For a dwelling unit....".
 
Clearly this is a load side Point of Connection. If it is a "dwelling unit""
then the 120% allowance is applicable. If it is not a "dwelling unit", then
there is no room to connect under NEC 2008.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  

 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
Sent: Friday, December 05, 2008 5:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] load side taps and NEC 240.21


Jerry - 

A line tap typically occurs between the utility meter and the main breaker -
not after the main breaker on the load side. It seems that you are
describing a load side tap which follows the 120% rule under 2008 NEC; I
might be misunderstanding the situation. Please clarify. There are few folks
out there who are able handle these large commercial grade interconnections
and I think it is well worth discussing.

Good luck! -August 


August Goers


Luminalt Energy Corporation
4000 Irving Street 
San Francisco, CA 94122


Office: 415.564.7652
Mobile: 415.559.1525
august at luminalt.com
www.luminalt.com



  _____  

From: William Miller <wrmiller at charter.net>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Friday, December 5, 2008 4:11:15 PM
Subject: Re: [RE-wrenches] load side taps and NEC 240.21

Jerry:

At a recent John Wiles seminar, John declared that this scenario is not a 
tap and is therefore not covered under the tap rule. This was news to me, 
but Wiles is considered some sort of guru in compliance discussions.

William Miller


At 03:43 PM 12/5/2008, you wrote:

>Wreches,
>
>
>I have a system where we are tapping onto the bus bars of a 1200 amp panel 
>fed by a 1200 amp main breaker. The easy place to tap onto the bus bars 
>is the load side of the breaker using the existing bolts.
>
>
>The inverter and utility fused disco are about 200 ft away, and the tap 
>conductors travel about15ft in EMT conduit before leaving the 
>building. After that the circuit is outdoors. NEC 240.21(B)5 allows taps 
>of unlimited length for conductors located outside of a building, except 
>at the point of load (in this case supply) termination.
>
>
>Can 20ft of conductor inside the building be covered by being "at the 
>point of load termination", or do I have to comply with NEC 240.21(B)2 and 
>have an OCPD within 25'?
>
>
>The construction foreman for this project is buddies with the inspector, 
>so getting a signed permit won't be a problem but I want this to be a code 
>compliant system. Can anyone lend some insight to the spirit of 
>240.21(B)2 and 5?
>
>
>Sorry if this has been discussed before, but searching didn't yield any 
>results.
>
>
>Best,
>
>Jerry Caldwell
>
>Recurrent Energy
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081205/2d4d86d7/attachment-0003.html>


More information about the RE-wrenches mailing list