620 VDC [RE-wrenches]
Bill Brooks
billbrooks7 at yahoo.com
Thu Jun 26 22:39:26 PDT 2008
Joel,
What does 600-Volts nominal mean to you? As Drake pointed out, 600Vac has a
peak voltage of 850V. Any momentary exceeding of 600V, when using reasonable
statistical design numbers, will be momentary at best and have no affect on
the equipment unless the equipment is faulty to start with.
Bill.
-----Original Message-----
From: Joel Davidson [mailto:joel.davidson at sbcglobal.net]
Sent: Thursday, June 26, 2008 6:43 PM
To: RE-wrenches at topica.com
Subject: Re: 620 VDC [RE-wrenches]
The NEC is very specific about 600 volts DC and AC in Chapter 1, paragraph
2. The 600-volt Rule is that fundamental. Almost all AWJ and Code Priests
interpret Article 690.7 "lowest expected ambient temperature" as the lowest
temperature recorded by their chosen Weather Scribes even if that low
temperature only happened once many years ago. From a practical standpoint,
some solar modules can not be used optimally with some inverters. Every time
I get a good module/inverter match, the manufacturers change specs,
availability, price, or all three.
----- Original Message -----
From: "Drake Chamberlin" <Drake.Chamberlin at redwoodalliance.org>
To: <RE-wrenches at topica.com>
Sent: Thursday, June 26, 2008 12:37 PM
Subject: 620 VDC [RE-wrenches]
>
> Hello Wrenches,
>
> Some inverters are able to withstand voltages above 600 VDC. The
> Solectria 95KW can take up to 620 VDC without harming the electronics.
>
> If we size a system so that the record low temperature is gives a voltage
> of under 620 VDC, a viable system can be installed. There is a question,
> however, about the Code compliance of this, since building wire is rated
> at 600 volts. Higher voltage wiring is available, but will likely not be
> cheap or convenient to use. Also, what about 600 V modules and PV cable?
>
> Since this is DC, there are not any cycles to create a voltage peak. A
> 600 VAC RMS nominal system can have (if my calculations are correct) a
> peak voltage of close to 850 volts. Also, system voltages can range up to
> 10% from the nominal, resulting in voltages of as high as 660 VAC RMS on
> 600 volt systems.
>
> The question is, "can we have a system with a possible low-temperature,
> open circuit voltage of 620 VDC with wiring and modules rated for 600
> volts? Can the other 20 volts be considered within the nominal range?
>
> Thanks,
>
> Drake
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list