Outback MX problem [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Wed May 28 22:47:12 PDT 2008
Matt,
Like Larry, I too challenge your question about "why you have the bulk point
set so high". You may not have read a recent Surrette Tech Bulletin #614
(not the much older #605), titled "Charging and Discharging Batteries;
Renewable Energy Applications". It calls for higher charge voltages: 29.4 is
a midpoint in Surrette's recommendations, and 30.0 the upper point. This
will vary according primarily to charging C/ rate.
Allan at Positive Energy
-----Original Message-----
From: Matt Tritt [mailto:solarone at charter.net]
Ron,
Since the MX thinks that the batteries are virtually full all the time,
"force bulk" is simply overriding the controller programming to effect a
charge, I would take OutBack up on the offer and call it good. I'm
curious as to why you have the bulk point set so high?
Matt T
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list