Apollo T-80 Alert [RE-wrenches]
Mick Abraham
mick at abrahamsolar.com
Fri May 9 06:37:41 PDT 2008
Hi, Wrenches~
The Apollo T-80 requires PV strings with more than 36 cells for every 12
volts of battery. I learned this while replacing a Trace C-40 control on
a 24 volt battery with "classic" array wiring (72 cells in each PV
string). (The array is 20 feet in the air and there were no funds to pay
for an array re-configuration.)
The Apollo unit would not work in this situation, and it took awhile to
figure out why. I finally installed a Xantrex XW-MPPT controller, and it
does work. Apollo's instruction book calls for at least 32 volts peak
power in order to charge a 24 volt battery. In additional testing at my
own la-bor-a-tree, however, an array providing 35 to 38 volts peak power
(in the cool morning) still couldn't drive normal operation with a 24
volt battery. The "35 to 38" volt number came off the XW controller
display, which again tested fine after the T-80 balked.
I have suggested to Apollo that the spec in their instruction book may
need revision, and I've also asked for better disclosure of this
characteristic on all Apollo sales information. Weeks later, I'm still
waiting for a response. Apollo did upgrade the hardware on this early
vintage controller at no charge and they updated the firmware, but then
they stopped answering my emails.
The T-80 may be a fine controller, but it is unsuitable for retrofit
unless the array can be rewired with higher voltage strings. Apollo
seems to find this unimportant; one of their techs even said that all
MPPT type controllers have the same issue.
Let's see: Outback, Blue Sky, BZ Products, and now Morningstar MPPT and
Phocos...all have peak tracking type controllers which can directly
replace a C-40 without changing the array...isn't that right? Apollo
needs to disclose this factor more fully, and ignore emails from a
concerned installer less fully.
Mick Abraham, Proprietor
www.abrahamsolar.com
P.S. If any of you would like to buy this demo controller, send me an
offer off list. I don't have the carton and the left side knockout has
been hammered out, but other than that it's in mint condition with a
blank warranty card.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list