I've inherited maintenance on a system with 2 Whisper 175's
(500lv)feeding a 48 volt battery bank that is inverted with parallel
SW5548's to an emergency panel. We have put a production meter in AC1
which now goes through an auto transfer switch to the emergency panel
when grid is out. The production meter is topping the batteries off,
since they are on standby only. I don't have any confidence in the
Whisper regulator, which is confirmed by the thread below. One is a EZ
wire (aluminum box), the other is a Whisper controller(black box). There
is no readout on the black Whisper Controller, just turn a tiny screw
and hope for the best!
Battery float and sell on the SW is 53.6. The Whisper Controller is
guestimated to be 57.6, its supposed to be higher than sell to grid
setting.
Since this system is 2.5 hrs away I can't monitor it and owner is
frequently not there. It may be working fine for all I know. I guess my
main concern is the production meter, which is at a premium rate,
spending too much time floating the batteries through AC1. Any
advice/comments?
Steve
************************************************
Fri 1/4/2008 3:54 PM
Has anyone used a substitute for Southwest's EZ wire system to regulate
battery charging, 24V on the 1000W machine?
I thought for a moment that a rectifier plus a Bergey 1kW controller
would look very similar.
thanks,
Erika
*********************
Ohio License # 44844
NABCEP Certified Solar PV Installer TM
Certified Home Energy Rater
___________________________________
Hi Erika,
The charge controls on EZWire systems are so poor and unreliable that I
have always simply used the rectifier part of their box and not wired up
the dump load circuit and hence don't use the charge control. We also
disconnected their meters too since the information was more misleading
than useful.
I then added another MPPT dump load controller to the system like the
Enermaxer when they were available. Now I would probably recommend an
MX60 if you can afford it and use it as a load control. Or simply use a
C40 or C60 in diversion mode.
Hope that helps!
Jeff C.
___________________________
HI Erika I agree with Jeff.
The rectifier is also very low amperage and do not survive storms very
well as they overheat and fail.
The Bergey is rather low cost and has a 100 amp rating instead of a 60
amp of the ez wire. The Dump load can be controlled using a Tristar 60
in diversion mode (Morning Star), which I perfer as I have had very good
luck with them.
Darryl
_________________________________________
The TriStar is also an excellent choice.
Matt T
Steve Johnson
LightWave Solar Electric
Nashville, Tennessee
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list