Grounding screw requirement [RE-wrenches]
Joe Felker
joe.felker at alumni.stevens-tech.edu
Thu Feb 21 11:06:59 PST 2008
Look in the 2008 code. That's what I quoted from...
Aaron Wellendorf wrote:
>
> Joe,
>
> The 2005 NEC 250.8 does not mention thread engagement standards, machine
> screws, or thread-forming screws. It requires use of a "listed means" of
> connection, no solder only connections, and forbids sheet metal screws.
> "Sheet metal screws shall not be used to connect grounding conductors or
> connection devices to enclosures."
>
> The "listed means" of connection most likely incorporates thread
> engagement standards in the listing testing process, but they are not
> spelled out. Probably because if you install the component in the listed
> manner you would meet the unstated standard. I would still like to know
> where an electrical thread engagement standard is found. I want to
> incorporate the standard into our training program. The NRTL's test to
> written standards and approve grounding connections and grounding kits
> (like Sq D's). Like Brian Wiley said, the standard may be mechanical and
> does not appear to be in the NEC.
>
> Thank you for pointing out the non-sheet metal screw requirement.
>
> Aaron Wellendorf
>
> Joe Felker wrote:
> <Look in 250.8 Connection of Grounding & Bonding Equipment
> <It permits the use of machine screws or thread-forming screws that
> <engage not less than two threads
>
>
Joe Felker
Engineering Manager
NABCEP Certified Solar PV Installer
The Solar Center
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list