Mark Frye wrote:
>
> The issue of the door grounding is interesting and the devil is in the
> details.
>
> Yes,a ground wire from the inverter to ground buss will ground the
> inverter, but what about the sheet metal of the door itself. This a
> piece of conductive material that could become energized, and must be
> properly ground at all times, door open or door closed.
I would use a screw with star washer to make sure the inverter is
connected electrically to the door, or backplate or whatever it is
mounted to.... Not just E-Panels.
boB
>
> A standard method is to install a stud into both the door and the box
> and use a braided ground strap to bond the door (see most Hoffman
> enclosure with hinged doors).
>
> Unless the door is properly bonded to the inverter chassis by some
> specific method, it sounds like the MidNite falls short in meeting this
> requirement.
>
> boB Gudgel wrote:
> >
> >
> > From Robin:
> >
> > Aint competition grand? Some of us handle it better than others I
> > guess.
> > I will address the issues that were brought up.
> >
> > AC bypass switch: This is a transfer switch. It does not need to be made
> >
> >
> > with circuit breakers. The MidNite bypass switch operates very smoothly
> > indeed. This is not an easy task. The AC bypass switches I designed at
> > Trace engineering, OutBack and MidNite are all similar, but slightly
> > different. They all meet the UL requirements and they all function
> > properly. It becomes a personal preference, not a safety or a NEC issue.
> >
> >
> > Transfer switches are not required to turn both circuits off at the same
> >
> >
> > time. Store bought transfer switches like the Square D at Trace work
> > like the MidNite bypass switch.
> >
> > Separate bypass switches: This style of bypass is not as convenient as
> > one that operates two or more inverters at the same time, but it is not
> > a safety issue. Fifty thousand bypass switches that work like the
> > MidNite bypass have been installed from Trace, Xantrex, OutBack and
> > Midnite over the last 13 years or so. Remember, we use breakers in
> > place of the switches, so in the unlikely event that something went
> > wrong, the breaker would trip. I am not aware of a single instance where
> >
> >
> > this style bypass switch led to a problem. In a previous post, I
> > mentioned an upcoming product that addresses the issue of single vs.
> > dual vs. quad bypass switches. What this means is that you will have
> > more choices available soon for larger systems. 95% of the E-Panel
> > installations have been single inverters. Dual E-Panel installations do
> > not yet have such a clear cost advantage over the competition as the
> > single E-Panel installs.
> >
> > Another accusation about our bypass switch has to do with moving both
> > the inverter output and the bypass breaker together at once. This is the
> >
> >
> > way we did it for years at OutBack and how it is now done at MidNite.
> > The OutBack bypass switches on dual and quads were changed to the
> > present configuration while I was still president of OutBack. I actually
> >
> >
> > made those changes. The reason for the change had nothing to do with
> > safety. We just couldnt get all the tolerances down to make a smooth
> > operating switch, so we opened up the slots. This forces the user to
> > manually turn the one switch on after flipping the slider. It also
> > allows both breakers to be turned off. Either method is ok. NEC requires
> >
> >
> > a separate generator disconnect box if the generator is not within site
> > or is remote. This is more convenient and more obvious as the AC input
> > disconnect if done separately. My electrician installed a separate
> > generator input disconnect before the PS2 panel to meet code since my
> > generator is remotely located. The PS2 can turn off both breakers at the
> >
> >
> > same time, but my electrician did not believe this was adequate. Some
> > installations do not require a separate generator disconnect due to
> > proximity.
> >
> > One more thought comes to mind to disconnect power
How about turning
> > the inverter off! Use the big DC breaker or the inverter on/off switch.
> > The output is then isolated by the contacts inside the inverter relay.
> > Some installers add a 50 amp output disconnect breaker inside the
> > E-Panel when needed. This is another way to create a clearly labeled
> > method to disconnect the house loads. Since the issue here is to make
> > sure there is no power going to the house loads it would be wise to turn
> >
> >
> > the generator off before working on the system. As discussed here, there
> >
> >
> > can be disconnects installed before or after the power source. This is
> > not a requirement of the E-Panel to meet code. Thousands of E-Panels
> > have now been installed and inspected without issues.
> >
> > Door grounding: The comment about our system being unsafe due to no
> > ground is false. Has anyone ever heard of putting a ground wire from the
> >
> >
> > equipment ground terminal on the inverter to the ground terminal in the
> > breaker box? All E-Panel doors come with a wiring diagram that clearly
> > shows the inverter grounded. Screws and star washers ground the inverter
> >
> >
> > to the chassis when shut, but to insure grounding while the door is
> > open, you should install a 6awg green THHN ground wire (follow the NEC
> > code). Equipment grounding is always required.
> >
> > Cabling: The cables that run from the battery breaker and shunt to the
> > inverter do not loosen up. This issue was addressed at the beginning
> > with ETL before I started designing the E-Panel. The statement that our
> > design is going to cause a fire is just not true. The E-Panel is a
> > different kind of breaker box. I knew people would be taking pot shots
> > at it, so ETL and I reviewed the cabling and wiring issues early on.
> > This is not something that was slipped by the ETL inspector while he
> > wasnt looking. I have been working with this same ETL engineer for over
> >
> >
> > a dozen years and believe me; he does not let anything through that does
> >
> >
> > not meet UL standards. Most of the Trace Engineering equipment, lots of
> > Xantrex, all of the OutBack, all of the Magnum, most of the PV Powered
> > and all of the Midnite products were evaluated by Tony Dorta of ETL.
> > Tony is very respected by manufacturers in the RE industry.
> >
> > The MidNite E-Panel does not hold as many breakers as other boxes. That
> > is true. The Stretched OutBack E-Panel will accept up to 6 additional
> > field installed din rail mount breakers and two panel mount breakers in
> > addition to the AC bypass, AC input and inverter battery breaker. The
> > stretched OB E-Panel has mounting for up to four shunts at once.
> >
> > Competition is good. False accusations are not. Per the moderators
> > request, this is a one time response. I consider this thread closed.
> > The market is pretty good at sorting out what they like.
> > I thank you for your support, past, present and future.
> > Robin Gudgel
> >
>
>
>
> Berkeley Solar Electric Systems
boB Gudgel K7IQ
MidNite/Magnum Solar/Energy
Washington AC
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list