With the generator input breaker off, switching to bypass shuts
everything off since you are bypassing to a de-energized circuit.
Todd
Christopher Freitas --- OutBack Power wrote:
>jay peltz wrote:
>
>
>
>>Whats funny is that Midnite solars box's work perfectly,
>>
>>
>
>Perfectly Huh? I strongly disagree - the Midnite AC bypass is not safe
>or compliant with the UL standards for a System Bypass or the NEC code
>because:
>
>The AC bypass bypass slider plate does not allow you to set both circuit
>breakers to the OFF position.
>
>It also does not allow the handle of the circuit breaker to indicate
>that it has tripped due to the extremely small opening for the handle in
>the AC bypass slider plate.
>
>The AC bypass slider plate also covers up the labeling on the breaker as
>to the amperage and on/ off status.
>
>I think these are serious safety issues with the Midnite product.
>
>Christopher Freitas
>OutBack Power Systems, Inc.
>cfreitas @ outbackpower.com
>www.outbackpower.com
>Arlington WA USA
>Tel 360 435 6030
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list