Keith,

The inspector is treating the system as a generator. This means the raceways
fall under the same requirements as a service entrance. Which means that, if
they're metal, you gotta bond them. Ground bushings &/or hubs at all
termination points.

Pray for Sun!

Matt Lafferty 
mlafferty at universalenergies.com 


-----Original Message-----
From: Keith Cronin [mailto:kcronin at islandenergy.net] 
Sent: Monday, November 12, 2007 3:25 PM
To: RE-wrenches at topica.com
Subject: Bonding of electrical equipment [RE-wrenches]

A topic came up today that I wanted to run by the team, electrically
speaking- NEC. An electrical inspector had a viewpoint that all conduit runs
from a main distribution system to our equipment- i.e.- disconnects and any
inverters or junction boxes needed to have bonding bushings as opposed to
standard locknuts with plastic bushings. These systems are grounded with the
appropriate grounding wiring sized per the NEC for the feeders. I have not
seen this requirement before and wanted to see what you all have experienced
in this environment.


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list