Outback generator support [WAS Advice sought for large off grid PV system;
Davis Terrell
davis at brightearthsolar.com
Mon Apr 2 12:59:25 PDT 2007
<x-flowed>
The FX will back off charging when passing through down to 5A AC (per
inverter I think), but if your loads + 5A > the generator CB rating then
your out of luck. (page 51 of the FX manual)
--
Davis Terrell
Bright Earth Solar
(802) 492-2273 / brightearthsolar.com
Jeff Wongstrom wrote:
>
>
> Thanks Allan, I am an Outback fan and appreciate the constructive
> criticism.
>
> I have this issue in an Outback system that originally had a single
> VFX 3524 and 800ah battery which had no problem with tripping the
> breakers of a 6.5KW Onan full output 120VAC. When a second inverter
> was added the generator breakers started to trip during the usual
> laundry and vacuuming routine. The 'solution' has been to drop the
> second charger out by turning down the charge rate. Unfortunately,
> this drops the charge rate back to less than C/10 as a single charger
> does not put out more than 70a. We do a lot of winter generator
> charging in NW Montana and do not mind hitting the batteries with C/5.
>
> I had thought that the charger would back off and allow the generator
> to power loads without tripping gen breakers by limiting generator
> input with AC2/GEN INPUT LIMIT. Is this the same as 'the inverter
> won't limit the pass-through load' ?
>
> Jeff Wongstrom
> NABCEP Certified Solar Installer
> Thirsty Lake Solar
> 406-889-5324
>
>
> On Apr 1, 2007, at 11:22 PM, Allan Sindelar wrote:
>
>>
>> No, Outback doesn't have generator support, at least not yet.
>>
>> The lack of generator support is a real issue. Somehow I just hadn't
>> realized the consequence of this, even after four years of working
>> with FX
>> inverters. So I am calling attention to this now so others don't make
>> the
>> same mistake.
>>
>> You can set the charge rate for the inverter, but you can't size the
>> inverter to optimize generator charging. This is because the inverter
>> won't
>> limit the pass-through load. Outback suggests about 50% overcapacity
>> beyond
>> what is necessary for charging.
>>
>> At our elevation range, a 3kW inverter-generator will put out around
>> 18-19A
>> AC continuous, which is ideally suited for charging with one Outback,
>> which
>> draws 19A maximum for charging purposes. However, if charging is set
>> at this
>> level, there is no headroom for additional pass-through loads.
>>
>> The Yamaha 3kW inverter-generator will just lug, I have learned,
>> until the
>> load is reduced. But the 3kW Honda inverter-generator will trip its
>> output
>> breaker, which requires manual restart of the gennie.
>>
>> I understand that Outback is working on this obvious shortcoming. My
>> hope is
>> that it will be available as a field upgrade, at least for existing
>> non-GT
>> models.
>>
>> For now, on the one single-FX off-grid system that has an existing 3kW
>> Honda, we instructed the customer to turn off the main AC load
>> breaker when
>> charging from the generator. It's a less than satisfactory solution,
>> but so
>> is arbitrarily turning down the charge rate.
>>
>> Be forewarned, and avoid my mistake.
>>
>> Allan at Positive Energy
>>
>> ----- Original Message -----
>> From: "William Miller" <wrmiller at charter.net>
>> Sent: Thursday, March 29, 2007 9:48 AM
>>>
>>> Outback has generator support? That is news to me! When did this
>>> occur?
>>>
>>> William Miller
>>>
>>>
>>> At 08:53 PM 3/28/2007, you wrote:
>>>
>>>> Outback and xantrex can support generator power, I
>>>> have a 3 phase support system that was originally to
>>>> be 55kW, and I found it to be cost effective up to the
>>>> 55 kW. Also Outback, and Xantrex, and SMA have
>>>> products that can generator support and inverter
>>>> support.
>>>>
>>>> What is wrong with using transformers?
>>>>
>>>> Darryl
>>
>
>
> --
> [Non-text portions of this message have been removed]
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list