Ken,

>From what I've seen, the XW charge controller has GFP built in to it, so if
you're using that controller, negative and ground must be kept isolated so
the GFP will work correctly, and probably for the controller to work at all.
If you're using a different charge controller, you'll be OK unless you want
GFP, in which case you may need to install a Midnite baby box and Midnite
GFP(s) and separate negative from ground, or some other kluge (and I mean
that in a GOOD way). As far as I can tell, a solid neutral-ground bond does
not adversely affect the inverter in any way.

The fact that Xantrex chose to use a GFP fuse inside the controller (and an
expensive 600 VDC KLKD fuse at that) instead of a separate breaker is a poor
call IMO. A ground fault anywhere in the system, not just in the array
wiring, will cost you the price of that fuse. Not sure what Xantrex has
planned for GFP in the new distribution panel when using somebody else's
charge controller either. Maybe ye olde Trace PVGFP from years back will
mount up to the DC breaker panel in the new enclosure, since it uses the
correct size breakers. It appears to still be available (that is, the manual
is not in the "discontinued products documents" list).

Looking forward to hearing your thoughts on the inverter.

Dan Rice
Abundant Sun, LLC.

----- Original Message ----- 
From: "Ken Schaal" <ken at commonwealthsolar.com>
To: <RE-wrenches at topica.com>
Sent: Monday, November 05, 2007 4:56 AM
Subject: Re: Xantrex XW [RE-wrenches]


|
| As I mentioned in my last post, we are doing a Y2K system upgrade so we
can
| net meter and have gen backup, at affordable prices.
| The 6048 XW is now on the wall and wired into the existing Trace DC
| disconnect and transfer switches. After wrestling the old Power Panel down
| off the wall---I use two 'farm jacks' for that joyful task---, it was a
| pleasure to bolt a bracket to the wall and lift the 125# XW into a slot on
| the bracket that carries the weight and then secure in the vertical
position
| with two screws at the top.
| Sweet!
| We will be finishing the install today I trust and start to play with it,
| although the net meter inspection and appropriate meter install is still
in
| progress.
| Our only hassle so far is due to our use of the existing DC disconnect,
and
| the fact that we will be adding an additional array, necessitating a
second
| charge control, both mounted above the Trace disconnect where the original
| C40's were mounted. The knockouts don't quite align, so we had to do a
| little grinding, about 3/8 ".
| The other thing we noticed is that the old Trace disconnect has common
| battery neg and equipment ground, where the new XW disconnect uses
seperate
| buses, with the battery neg isolated. Any thoughts on how big an issue
this
| is?
| The new XW distribution panel is quite complete with transfer breakers,
nice
| flex wire, etc but does cost $1K, so the temptation for many will be to
use
| the existing Trace.
|
| More thoughts to follow after we try it out with the existing array.
|
| Ken Schaal
| CommonWealth Solar
|
| ----- Original Message ----- 
| From: <i2p at aol.com>
| To: <RE-wrenches at topica.com>
| Sent: Sunday, November 04, 2007 3:15 PM
| Subject: Re: Xantrex XW [RE-wrenches]
|
|
| >
| >
| >
| > In a message dated 11/3/2007 6:34:33 A.M. Pacific Standard Time,
| > jay at asis.com writes:
| >
| > What are  the comments about the new XW equipment.
| >
| >
| >
| > Me too, waiting.
| >
| > Don L
| >
| >


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list