Outback Power AC voltage fluctuation [RE-wrenches]
Jason Lerner
wapalco at gmail.com
Wed Aug 22 07:58:58 PDT 2007
<x-flowed>
Hello Jay,
I had a similar situation with a quad stack. I adjusted the output
voltage of each VFX to the Fluke (there was quite a range), and then
calibrated the Mate to show the Fluke Voltage, and then put the VFX
that had the most different voltage in port #4 to come on last, and
everything works pretty good now. Maybe you could tune the output
voltage with enough room to avoid the fridge fan coming on?
Best,
Jason Lerner
Waldron Power and Light Co.
On Aug 21, 2007, at 7:51 PM, Jay Peltz, Peltz Power wrote:
>
> Hi All,
>
> I've got a Dual PP VFX 3524 with 3000 amp hr battery new system.
> Yep same one that I was called out on.
>
> I've fixed most of the problems but I can't seem to understand or
> fix the following.
>
> The AC volts will fluctuate 3-5v with no load change. It'll hold
> steady for a bit, minute or two, then in the space of
> 10 seconds it'll do its 3-5v deal, then back.
> Also I've got up to 9v difference between what the Mate says and
> what the volts are actual.
> ( all measurements with Fluke 87)
>
> And when the AC loads go up the voltage numbers can get even more
> extreme, and be either higher or lower than what the mate says.
>
> Mostly the customer wouldn't care, but the darn fan in the
> refrigerator keeps going up and down, drives him crazy.
>
> Outback Tech support says this is normal, may be but I haven't seen
> this on any of the many multi inverter systems I've installed.
>
> Any ideas or experiences?
>
> thanks,
> jay
>
> peltz power
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
</x-flowed>
More information about the RE-wrenches
mailing list