Kurt,

I don't think the requirement for metallic raceway is based on the location
of fusing, if any.  Rather, the requirement for metallic raceway is based on
which Code cycle you are on and the location of the PV DC Disconnect
relative to the building.

If you are on NEC 2002, then you have no requirement for metallic raceway
anywhere.  However, the PV DC Disconnect must be located outside of the
building or inside nearest the point of entry of the DC conductors.

If you are on NEC 2005, you can put the PV DC Disconnect inside, remote from
the point of entry of the DC conductors, but the DC conductors must be in
metallic raceway from the point of entry to the disconnect.

Mark Frye

-----Original Message-----
From: Mike Bernhard [mailto:spaight12 at sbcglobal.net]
Sent: Tuesday, July 10, 2007 4:27 AM
To: RE-wrenches at topica.com
Subject: Re: Inverter location [RE-wrenches]



Kurt,
The output (A/C) of the inverter can be installed in any approved raceway or
cable assembly.  PVC (sch 80 if exposed) is an approved method.  The metal
raceway rule only applies to the unfused D/C output of the array.  If you
are installing a high voltage system, the voltage drop is similar for A/C or
D/C. Either way would work.
Mike Bernhard


----- Original Message -----
From: "Kurt Nelson" <sunwise at cheqnet.net>
To: <RE-wrenches at topica.com>
Sent: Monday, July 09, 2007 2:59 PM
Subject: Inverter location [RE-wrenches]


>
> Greetings all,
>
> I'm doing a 3,200 watt pole mounted system with an SMA inverter.  It
> looks like I can have the inverter out at the array, or indoors by the
> service entrance.
>
> Does the code require metallic conduit inside the building in either
> case, or if it is the ac output of the inverter (mounted out at the
> array), can it be in PVC and/or within wall cavities, etc.?
>
> Which location do most folks prefer.
>
> Thanks in advance,
>
> Kurt
>
> ----------------------------------------------------------------
>
> Kurt Nelson
> PO Box 309
> Cornucopia, WI 54827
> 715-742-3406
> sunwise at cheqnet.net
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------








More information about the RE-wrenches mailing list