The purpose behind putting source/output circuits in metal conduit in a 
building has to do with the conductors being treated as Service Entrance 
Conductors.  The SEC rule in WI is 8 ft inside the bldg to the first 
disconnecting means.  The metal raceway provision is a way around the SEC 
rule.  If you have a fused disconnect outside and have included an equip. 
gnd cond in the raceway from the array and are continuing it to the inverter 
the conductors are now feeder conductors.  Try this arguement on your AHJ. 
Just make sure to quote all appropriate code articles.(Services, Grounding 
and PV).
Mike Bernhard
----- Original Message ----- 
From: "Mark Frye" <markf at berkeleysolar.com>
To: <RE-wrenches at topica.com>
Sent: Tuesday, July 10, 2007 9:33 AM
Subject: RE: Inverter location [RE-wrenches]


>
> Kurt,
>
> I don't think the requirement for metallic raceway is based on the 
> location
> of fusing, if any.  Rather, the requirement for metallic raceway is based 
> on
> which Code cycle you are on and the location of the PV DC Disconnect
> relative to the building.
>
> If you are on NEC 2002, then you have no requirement for metallic raceway
> anywhere.  However, the PV DC Disconnect must be located outside of the
> building or inside nearest the point of entry of the DC conductors.
>
> If you are on NEC 2005, you can put the PV DC Disconnect inside, remote 
> from
> the point of entry of the DC conductors, but the DC conductors must be in
> metallic raceway from the point of entry to the disconnect.
>
> Mark Frye
>
> -----Original Message-----
> From: Mike Bernhard [mailto:spaight12 at sbcglobal.net]
> Sent: Tuesday, July 10, 2007 4:27 AM
> To: RE-wrenches at topica.com
> Subject: Re: Inverter location [RE-wrenches]
>
>
>
> Kurt,
> The output (A/C) of the inverter can be installed in any approved raceway 
> or
> cable assembly.  PVC (sch 80 if exposed) is an approved method.  The metal
> raceway rule only applies to the unfused D/C output of the array.  If you
> are installing a high voltage system, the voltage drop is similar for A/C 
> or
> D/C. Either way would work.
> Mike Bernhard
>
>
> ----- Original Message -----
> From: "Kurt Nelson" <sunwise at cheqnet.net>
> To: <RE-wrenches at topica.com>
> Sent: Monday, July 09, 2007 2:59 PM
> Subject: Inverter location [RE-wrenches]
>
>
>>
>> Greetings all,
>>
>> I'm doing a 3,200 watt pole mounted system with an SMA inverter.  It
>> looks like I can have the inverter out at the array, or indoors by the
>> service entrance.
>>
>> Does the code require metallic conduit inside the building in either
>> case, or if it is the ac output of the inverter (mounted out at the
>> array), can it be in PVC and/or within wall cavities, etc.?
>>
>> Which location do most folks prefer.
>>
>> Thanks in advance,
>>
>> Kurt
>>
>> ----------------------------------------------------------------
>>
>> Kurt Nelson
>> PO Box 309
>> Cornucopia, WI 54827
>> 715-742-3406
>> sunwise at cheqnet.net
>>
>>
>> - - - -
>> Hosted by Home Power magazine
>>
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
>> http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & how to change your email address:
>> www.mrsharkey.com/wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>>
>>
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: 
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>
> 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>



More information about the RE-wrenches mailing list